Taco 571 Zone Valve

I have a problem with a Taco 571 Zone Valve. I had a broken valve and had to replace the head of the valve (the electric part which connects to the wires) and I did that. However, the head warms up excesivelly and still does not work (does not let any hot water through the system) as a result the heating in that zone does not work. Does that indicate an electrical problem (my other two valves are working fine) or does that mean that I will have to replace the whole valve (including the water part)? Thank you everyone. Frustrated and cold.
 

Last edited by stefanov; 03-18-05 at 01:09 PM.
Sponsored Links
  #2  
Old 03-18-05, 07:49 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,936
Received 1 Vote on 1 Post
Taco zone valve

Can you open the valve manually? If you cannot, the valve mechanism is stuck & the whole valve will need to be replaced.
 
  #3  
Old 03-18-05, 07:55 PM
Member
Join Date: Feb 2005
Location: Massachusetts
Posts: 123
Received 0 Votes on 0 Posts
Make sure the heat anticipator inside the thermostat is set for .9 What kind of thermostat do you have
 