Replaced aquastat relay on gas fired boiler and pilot will not stay lit

Reply

  #1  
Old 04-21-05, 04:11 PM
rodcma
Visiting Guest
Posts: n/a
Replaced aquastat relay on gas fired boiler and pilot will not stay lit

I replaced the 5 year old L8124C aquastat relay after the gas fired boiler would not fire when the tankless water heater was called upon for hot water. After making the repair I could not get the gas pilot to stay lit so I replaced the Honeywell Q313B thermopile. The new thermopile is putting out .823 volts to the gas valve but the pilot will still not stay lit. Question: Should I replace the gas valve next or is there another part of this Burnham 404B boiler that could cause this problem?
 
Sponsored Links
  #2  
Old 04-23-05, 04:42 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,943
Received 5 Votes on 5 Posts
Pilot

Are you sure this is the right thermopile for the gas vavle? Most gas valves only require a 30 mV thermocouple. Numbers from the gas valve would help. Make sure the pilot is strong & hitting the thermopile.
 