Air in circulating system


  #1  
Old 06-05-05, 05:55 PM
jariggs104
Visiting Guest
Posts: n/a
Air in circulating system

I have a Gas heating system,two zones, propane..had to replace one circulating pump... it was necessary to drain the system..I seem to be unable to remove the air in the system controled by the new pump...This is an older home and there are air valves attached to the radiators in that system and I am able to bleed them...but not so in the newer system... The pump works but is not circulating the water... How can I bleed that zone?... thanks
 
  #2  
Old 06-07-05, 04:24 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Air in system

Somewhere above the circulator should be a shut off valve & another valve with a garden hose connection. Turn off the valve, attach a hose to the valve with the garden hose threads. Open the garden hose valve (boiler drain). Allow water to flow until you don't get bubbles. If you can take some pictures & provide a link to them it would be a lot easier to explain.
 
  #3  
Old 06-07-05, 07:31 PM
jariggs104
Visiting Guest
Posts: n/a
J. Riggles

Grady:

You made it very clear about removing air from my system. Thanks a lot... J.riggles@comcast.net
 
 