I have 3 zones in my system and the first 2 purged fine. I got all the air out and everything was heating up nice with no noise. then I went to do the third zone (upstairs bedrooms) and when I opened the valve nothing came out... nothing! I am doing it the same way as the other 2 so what gives? I even left it open for a bit and waited and still nothing.
Old 10-07-05, 04:29 PM
Grady's Avatar
Received 35 Votes on 33 Posts
Nothing from purge valve
The boiler pressure may be too low to push the water that high. Crank it up to 20-25 psig for purging purposes only. After the air comes out turn it back down to around 15.
Old 10-07-05, 04:31 PM
Ed Imeduc's Avatar
Wink
Is the auto fill on???? What is the boiler psi .Need to 2nd floor should be around 18 psi.
ED
Old 10-07-05, 04:34 PM
JTW4462
Boiler preasure was up around 30 and the auto fill is open. The preasure is almost always that high... I don't know how to adjust it.
Old 10-07-05, 04:46 PM
Grady's Avatar
Boiler pressure
Pressure should NOT be that high. Use a tire gauge to check the pressure on the diaphragm tank. It will be the same as the system pressure. Post back with results.
Old 10-07-05, 04:49 PM
JTW4462
ok... well the preasure on the tank is always like 12-15 but the preasure/temp gauge on the boiler is always higher..
Old 10-07-05, 05:04 PM
Grady's Avatar
gauge
The gauge is lying to you. A common problem. Does your bladder tank look like this: http://www.amtrol.com/filltrol.htm
Old 10-07-05, 06:10 PM
JTW4462
yea... it's T H I S
Old 10-07-05, 06:17 PM
Grady's Avatar
Good shot
Good pic & a bonus. That red device above & right of the tank is the water feeder. Loosen the lock nut on top & turn the screw in about 1 1/2 turns. Check the pressure on the tank & if not up to 20-25 turn the screw in 1/2 turn at a time until you get there. Give the feeder 1-2 minutes between adjusting & checking the pressure. When done purging, be sure to turn the pressure back down to about 15.
Old 10-07-05, 06:26 PM
JTW4462
Old 10-08-05, 09:30 AM
Grady's Avatar
Pics
In the pic labeled Main pump, I don't like the looks of the lower part of the boiler. It looks like it has been VERY hot. I strongly suggest you get a pro in there to look at it before you have a fire or are asphyxiated.
Old 10-08-05, 03:43 PM
JTW4462
what part are you looking at specificaly?
Old 10-08-05, 04:48 PM
Grady's Avatar
Hot spot
In the photo labeled "main pump", I'm looking left of the pump at what appears to be the lower part of the boiler. It looks as if it has been very hot, to the point of blistering the paint.
Old 10-10-05, 08:55 PM
JTW4462
It's just filthy.