Help with zone valves

Thanks for such a great site.I have a oil fired boiler with a Honeywell L8024A triple aquastat relay,on a single zone.I split the system into two zones,installed zone valves V8043G. The problem is I do not have the instructions to wire these valves into the aquastat. Any help would be appreciated.
Thanks Skidder
 
  #2  
Old 10-17-05, 07:01 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Wiring zone valves

Here is a link in which there is a wiring diagram showing exactly how to do it.
http://www.crownboiler.com/Manuals/C...structions.pdf
 
  #3  
Old 10-18-05, 03:42 AM
S
Member
Thread Starter
Join Date: Oct 2005
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Grady,that link shows a different aquastat and zone valves but it gives me enough info to make it work.
Thanks Skidder
 
  #4  
Old 10-18-05, 06:54 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Aquastat

The L8124 is just an updated version of the L8024. The big caution is not to try to power the zone valves off of the aquastat. Use a separate transformer.
 
 