Please comment on my boiler setup drawings/plans


  #1  
Old 10-20-05, 05:45 PM
S
Member
Thread Starter
Join Date: Aug 2005
Location: Philadelphia area
Posts: 31
Upvotes: 0
Received 0 Upvotes on 0 Posts
Lightbulb Please comment on my boiler setup drawings/plans

I am getting ready to install my heating/hot water system! I produced detailed drawings of the system. Could you please review and comment:
Closed circuit piping diagram:
http://www.geocities.com/slvr00gt/My_boiler_setup.gif
Electrical diagram:
http://www.geocities.com/slvr00gt/My...electrical.gif
Relative position of the components and piping diagram :
http://www.geocities.com/slvr00gt/ho...iler_setup.gif
Bill of materials ( doesn't include boiler, WH, circulators):
http://www.geocities.com/slvr00gt/materials.doc

Thank you very much!
 
  #2  
Old 10-20-05, 07:19 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Diagrams

Piping looks fine, as far as I can tell.

Wiring: Why are you using Y, G, & C on a boiler system? Must admit I know nothing about the Peerless Pinacle.
 
  #3  
Old 10-20-05, 07:41 PM
S
Member
Thread Starter
Join Date: Aug 2005
Location: Philadelphia area
Posts: 31
Upvotes: 0
Received 0 Upvotes on 0 Posts
You are right, I double-checked, Wires W and R should go to boiler

I didn't mention anywhere, but I have spacepak mini-duct AC system installed with ESP-2430D condensor and Lennox compressor units. I will be installing matching hot water coil ( HWC-2430D ) to the condensor/blower unit. Therefore, condesor/blower/hot water coil will be wired to the thermostat for both cool and heat

Thanks!
 

Last edited by slvr00gt; 10-21-05 at 07:25 PM.
  #4  
Old 10-21-05, 06:59 PM
S
Member
Thread Starter
Join Date: Aug 2005
Location: Philadelphia area
Posts: 31
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question

Originally Posted by Grady
Piping looks fine, as far as I can tell.

Wiring: Why are you using Y, G, & C on a boiler system? Must admit I know nothing about the Peerless Pinacle.

I went to the plumbing store to order materials and talked to HVAC cosultant, guy with 30 years in the industry, who was suprisingly eager to help! ( normally I run into the wall when I try to talk to pros and they sense amature, detailed drawings probably helped to aliviate hostility)

I got two suggestions that seemed usefull:
1) Don't use type L piping, but stick with thinner type M. He said, it will limit heat loses ( energy taken to heat the pipe)

2) don't use 1/2" pipe for heating coil zone nor 3/4" for water heater zone. Use 1" for zone piping, it will help with heat transfer to the zone.

3) he strongly recommended the use of boiler reset controller ( such as PC702)

I got another suggestion from him that perplexed me:
1) He was strongly against supply/return feedback ( this "closely spaced tees" configuration) he argued that at best it is not necessary and at worst it would not work right.....


What do you think?
( I updated the diagrams to reflect suggestions)
 

Last edited by slvr00gt; 10-21-05 at 07:31 PM.
  #5  
Old 10-21-05, 07:48 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Piping

I agree on using Type M copper (good bit cheaper & L is overkill).
Insulate your pipes to reduce heat loss.
For the indirect: 1" is probably better.
For the heating zones unless they are very long or have a lot of elbows, 3/4" is probably ok but 1" won't hurt.
Boiler reset controls are nice & can save on operating cost. Just be sure to get one in which the reset is overridden on a call for domestic hot water.
As far as the closely spaced tees: I say to do whatever the manufacturer calls for. If you don't, this gives them an "out" if there is a warranty issue.
 
 