Boiler temp and pressure problems


  #1  
Old 10-26-05, 05:59 PM
T
Member
Thread Starter
Join Date: Jun 2005
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Boiler temp and pressure problems

Purchased a 1920's Victorian with hot water heat system that heats first and second floors. The entire system runs off one thermostat on the first floor. It's an American Standard Boiler, but I'm not sure of the year. Ayway, here the problem..... whenever I turn the boiler temp up above 140 degrees the pressure gauge on the boiler goes up near 50 pounds, also the system pressure gauge rises to 30 pounds and will often cause the relief valve to start spitting water. So here is my questions?
1 - At what temp should a hot water system operate normally
2- Why an I getting this pressure build up
3- Is there any way a DIY can fix it

Any help would be appreciated, Thanks
 
  #2  
Old 10-26-05, 07:23 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Low temp - high pressure

It sounds like your expansion tank may be flooded or nearly so. If it is a conventional tank with a hose bib on it, there should be some sort of shut off valve between the tank & the boiler. Close the shut off valve, attach a hose to the hose bib, open the hose bib, & drain the tank completely. Once drained, reverse the process, opening the shut off slowly while trying to maintain about 15 psig on the boiler.

"Normal" temperature for a hot water boiler is about 180.
 
 