thermostats


  #1  
Old 11-20-05, 05:28 AM
M
Member
Thread Starter
Join Date: Sep 2005
Posts: 44
Upvotes: 0
Received 0 Upvotes on 0 Posts
thermostats

hi i just replaced the two thermostats on my hot water system.not looking at where the wires were on the old one .one red one white wire.now the real problem when the upstairs zone is calling for heat it comes on and the lower
zone is off.bout when the lower zone comes on calling for heat both zone valves
are open and both get heat even though the thermostat on the upstairs
shows heat off.i have two honeywell model rth5100b thermostats and two
taco model #571 zone valves running off one taco model 008-f2 circulator.
 
  #2  
Old 11-20-05, 05:49 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
zone valves

Many digital thermostats are not compatable with heat motor zone valves. I don't know about your particular stats. The red wire should go to terminal RH & the white to terminal W.
 
  #3  
Old 11-21-05, 05:39 AM
M
Member
Thread Starter
Join Date: Sep 2005
Posts: 44
Upvotes: 0
Received 0 Upvotes on 0 Posts
thats how they are.thanks i'll keep and eyeon it seems like sometimes it
works right and other times not.
 
 