Trying to charge a drained system

Hi all-

I bought a house that has hw baseboard and it looks like the previous owner just using it for HW I have dedcided to use the baseboard also. How do I charge the system. It is not a closed system, it is connected to the cold water line. I cannot seem to get the water to any of the baseboards. The water does not seem to be going into the system past the circulator. Also when I open the fast fill nothing happens. Any ideas? This in only going to be temporary heat while I install a new boiler.
 
  #2  
Old 11-24-05, 11:31 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,381
Received 35 Votes on 33 Posts
Sign Man

If you have zone valves they will need to be open when filling the system.
 
 