weil mclain boiler model pd6,pilot wont stay lit after 60 sec.

I have a weil mclain boiler (older model pd6). The pilot wont stay lit after the 60 seconds. Have held it for as much as 5 minutes. help! getting cold
 
  #2  
Old 01-16-06, 04:06 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Pilot problem

The thermocouple is probably bad. The usually cost less than $10 and are avilable at any home center. Make sure the pilot flame hits at least the top 1/3 of the thermocouple.
 
  #3  
Old 01-16-06, 04:12 PM
O
Member
Thread Starter
Join Date: Jan 2006
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
grady

The thermocouple you said is available, what would I ask for?
 
  #4  
Old 01-16-06, 06:03 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Thermocouple

Ask for a thermocouple. They come in various lengths. It would be best to take the old one with you. The length is not critical as long as it is long enough.
 
  #5  
Old 11-04-10, 08:28 PM
A
Member
Join Date: Nov 2010
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Need Help With a Weil McLain CG (series 11) Boiler Pilot will not stay lit

I happen to have a Weil Mc Lain Boiler Model CG (series 11) Boiler pilot was out and found Thermalcouple was bad Replaced Thermalcouple and pilot will not stay lit. Any help will be greatly appreciated..
 
  #6  
Old 11-05-10, 08:48 AM
M
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes on 0 Posts
Albert, you hi-jacked the thread - but since it's so old, there should be no confusion.

How long does the pilot stay lit before it goes out?

Is the tip of the thermocouple in the pilot flame? The size of the pilot flame can be adjusted - the adjustment screw is usually under a larger screw-head on the gas valve.

If that's OK, disconnect the t-couple from the gas valve. Have an assistant hold down the push button, and measure the DC voltage across the t-couple contacts.
 
 