low water cutoff

i have a gas furnace,steam radiators. My low water cutoff has started clicking on and off steadily until 1 of 2 things happen. 1) heat comes on 2) i drain water until low water cutoff comes on. I don't see surge in the guage glass. Could it be just the cutoff switch itself?
 
  #2  
Old 01-28-06, 04:31 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,245
Likes: 0
Received 0 Likes on 0 Posts
If the system is overfilling, you have a problem with the feed valve or float switch depending on the type of water feeder. You can close off the water valve and see if things settle down. A steam system that works correctly needs very little water from week to week.

Ken
 
  #3  
Old 01-29-06, 11:54 AM
L
Member
Thread Starter
Join Date: Jan 2006
Posts: 2
Likes: 0
Received 0 Likes on 0 Posts
there is no problem with overfilling
 
  #4  
Old 01-31-06, 08:16 PM
H
Member
Join Date: Nov 2005
Location: usa
Posts: 54
Likes: 0
Received 0 Likes on 0 Posts
Originally Posted by lnmn
i have a gas furnace,steam radiators. My low water cutoff has started clicking on and off steadily until 1 of 2 things happen. 1) heat comes on 2) i drain water until low water cutoff comes on. I don't see surge in the guage glass. Could it be just the cutoff switch itself?
lwc needs to be cleaned you have to take it apart
 
 