low water cutoff

i have a gas furnace,steam radiators. My low water cutoff has started clicking on and off steadily until 1 of 2 things happen. 1) heat comes on 2) i drain water until low water cutoff comes on. I don't see surge in the guage glass. Could it be just the cutoff switch itself?
 
Sponsored Links
  #2  
Old 01-28-06, 04:31 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,245
Received 0 Votes on 0 Posts
If the system is overfilling, you have a problem with the feed valve or float switch depending on the type of water feeder. You can close off the water valve and see if things settle down. A steam system that works correctly needs very little water from week to week.

Ken
 
  #3  
Old 01-29-06, 11:54 AM
Member
Thread Starter
Join Date: Jan 2006
Posts: 2
Received 0 Votes on 0 Posts
there is no problem with overfilling
 
  #4  
Old 01-31-06, 08:16 PM
Member
Join Date: Nov 2005
Location: usa
Posts: 54
Received 0 Votes on 0 Posts
Originally Posted by lnmn
i have a gas furnace,steam radiators. My low water cutoff has started clicking on and off steadily until 1 of 2 things happen. 1) heat comes on 2) i drain water until low water cutoff comes on. I don't see surge in the guage glass. Could it be just the cutoff switch itself?
lwc needs to be cleaned you have to take it apart
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: