Circulator Keeps Running
#1
Member
Thread Starter
Join Date: Nov 2005
Location: nassau county ny
Posts: 177
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Circulator Keeps Running
I have a 3 zone oil boiler with baseboard radiators, I installed 3 luxpro line voltage thermostats about a month ago but all of a sudden the main floor zone keeps running. I snapped the thermostat body out of the housing and it still runs, the room shows 75 and the thermostat in set for "70 Hold" the only way to stop the circulator was to shut the main boiler switch off. Any ideas or suggestions?
#3
Member
Thread Starter
Join Date: Nov 2005
Location: nassau county ny
Posts: 177
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the reply I have 3 circulators each controlled by a seperate line voltage LUXPRO thermostat. I had to use the reset button and the circulator stopped right away so now I just have to reprogram it. I guess like any othe relectronic device it must have taken a power hit and got messed up so now I'm back. Thanks