Water Pressure in Boiler


  #1  
Old 04-17-06, 02:31 PM
T
Member
Thread Starter
Join Date: Apr 2006
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Water Pressure in Boiler

I recently had to replace my expansion tank and now I can't regulate the pressure in the boiler. It goes from 0 psi when cold to 30 psi when hot. I have added pressure to the expansion tank and then reduced it. The last time I messed with it, I added water until the relief valve popped but the pressure reading was still 0 PSI. But, when the boiler warmed up, it went back up to 30 PSI and only discharged a small amount from the relief valve. If I test the pressure in the Expansion tank with a tire guage it reads about 18 when cold and 28 when hot. Would a faulty presure guage behave this way? If I replace the combination temperature/pressure guage do I have to drain the boiler again? The boiler is a Peerless and I'm using it in a two story house with radient floor heat.

I can't figure out what I'm doing wrong and would appreciate any advice.

Thanks.
 
  #2  
Old 04-17-06, 04:24 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
TimR

Remove the tank from the system & check the pressure. It should be about 12# for up to a two story house. By removing the tank you can verify the bladder is good. If it is, you probably have a faulty gauge.
 
 