relay question


  #1  
Old 09-05-06, 05:42 PM
F
Member
Thread Starter
Join Date: Jan 2003
Posts: 24
Upvotes: 0
Received 0 Upvotes on 0 Posts
relay question

Hello, I am wiring a new Dunkirk boiler, with two zone valves(honeywell 4 wire) and one circulator pump. The handy box on the side of the boiler has 3 pairs of wires, 2 yellow labeled THERMOSTAT, a black and white labled CIRC. PUMP, and a black and white labled POWER, IS IT NECESSARY TO HOOK UP A RELAY BOARD FOR THIS SYSTEM ?( I have the ARGO AR861-2).
When I feed the bioler power leads with 110V, the yellow stat wires will supply 24v to my two thermostats, and I could control the zone valves through them. (not utilizing the end switches), The circ. pump would be wired directly to the appropriate leads, seems I would not need the relay at all, is this correct?

Thank You, fbar.
 
  #2  
Old 09-05-06, 06:11 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,674
Received 40 Upvotes on 38 Posts
Argo 861

This relay is intended for systems using multiple circulators. Do not use it on a zone valve system.
 
  #3  
Old 09-05-06, 07:19 PM
F
Member
Thread Starter
Join Date: Jan 2003
Posts: 24
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Grady, Am I correct in saying I dont need a relay at All?
 
  #4  
Old 09-05-06, 07:23 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,674
Received 40 Upvotes on 38 Posts
Relay

You are correct. It does not need a relay. Depending on the aquastat, you may need to install a 40 VA transformer to power the zone valves.
 
 