Balancing Zones

Reply

  #1  
Old 10-10-06, 07:15 PM
R
Member
Thread Starter
Join Date: Aug 2006
Location: usa
Posts: 902
Received 0 Votes on 0 Posts
Balancing Zones

I have three zone hydronic system. One zone (smallest) is a hobby/computer room, around 220 square feet, with about 30 or so feet of fin tube for heating. The circulator for all three zones is a Taco 007. Main house is about 1300 square feet (largest zone, CI baseboard), and the second largest zone is about 400 square feet with a mix of CI baseboard and some fin tube at the start of the supply feed where the water is hottest. Only priority is for the DHW indirect.

Should I play with the zone balancing adjustments on the valves to reduce the flow rate on the smaller zones? I'm using Grundfos zone valves, which I think are rebadged Sparco/Honeywell Powertracks. Previously I had two circulators, one for the main house, and a second one for the smaller zones with Taco heat-motor zone valves. Everything worked in the past without doing anything to balance the zones, but this is a new system. Any suggestions on what to try for initial settings?

Pete
 
Sponsored Links
  #2  
Old 10-10-06, 07:32 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,253
Received 23 Votes on 21 Posts
Balancing

As a wise man once said; "If it ain't broke, don't fix it".
Let it go for a while then if you find a gross imbalance, we can address that issue when it comes up.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: