What is that buzz????

Lately, during the early mornings when the house is quiet, I sometimes hear buzzing sound that I believe is related to the boiler. Our bedroom is on the second floor opposite side of the house from the boiler in the basement. But, when the boiler starts up, I can hear it. Occasionally, a few seconds after the boiler starts up, a buzzing sound can be heard. The sound lasts a few seconds and stops when the boiler shuts down. To me, the buzz sounds like electricity, kind of like a bug getting zapped. My husband heard it once and said it sounded like buzzing. This does not happen all the time. I don't hear this sound during the day. What can it be? Can it be vibration? What can be wrong with the boiler? Thanks.
 
  #2  
Old 11-21-06, 02:55 PM
H
Member
Join Date: Oct 2006
Location: USA
Posts: 56
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is this an oil or gas boiler?
 
  #3  
Old 11-21-06, 03:39 PM
N
Member
Thread Starter
Join Date: Jul 2005
Location: NJ
Posts: 261
Upvotes: 0
Received 0 Upvotes on 0 Posts
It is a P-WGO-6 Weil Mclain oil boiler.
 
  #4  
Old 11-21-06, 04:07 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Try to localize the noise a bit... that might help getting answers, but it could be a vibration caused by one of the control transformers... or, maybe the oil lines are vibrating against something... or, could be a vibration caused by the circulator and transmitted on the water piping... or...

soooo, see if you can get even a little more local with the noise and tell us what ya find.
 
  #5  
Old 11-21-06, 04:11 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

Occasionally, a few seconds after the boiler starts up, a buzzing sound can be heard. The sound lasts a few seconds and stops when the boiler shuts down.
??? Is it the whole time the burner is on or not??
 
  #6  
Old 11-21-06, 04:13 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Originally Posted by Novice134
...Occasionally, a few seconds after the boiler starts up, a buzzing sound can be heard. The sound lasts a few seconds and stops when the boiler shuts down. To me, the buzz sounds like electricity, kind of like a bug getting zapped. ...
Ya know, I just re-read this part and am wondering if it's possible that your ignition is somehow arcing to something and you are hearing that ? I think I'd call my service guy if I were you and have him take a look-see... if you can hear it on the other side of the house, in a bedroom, I'm thinkin' it might be pretty loud at the boiler!

Have you got zones, etc ? Describe what you know of your system... how old is the boiler? When was the last time you had it serviced ?

Ed, ya know that occured to me too... I wonder if the burner is short-cycling ??? maybe the circulator coupling is gone ??? or maybe the burner coupling ???
 
  #7  
Old 11-21-06, 04:23 PM
Join Date: Aug 2006
Location: usa
Posts: 839
Upvotes: 0
Received 0 Upvotes on 0 Posts
boiler noise

Think it could be caused by mineral buildup in the boiler as well... IIRC...

Pete
 
  #8  
Old 11-21-06, 05:40 PM
N
Member
Thread Starter
Join Date: Jul 2005
Location: NJ
Posts: 261
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ed, I believe the buzzing sound is heard only when the boiler kicks on in early morning. Once the boiler shuts off, the buzz disappears.

NJ Trooper, the boiler is about 8 years old. We have multiple zones in the house. We had our annual tune up in mid Sept. Right before the annual tune-up, our aqua-stat failed and was replaced.

Trying to localize the noise is tough. The only time I can hear this buzzing is in early morning. And, I don't hear it all the time. Since the duration of the noise is very short, by the time I get to the stairs, it will have stopped. However, I have yet to hear the buzzing during the day or evening when I am downstairs. Even when I stopped everything when the boiler kicks on, I will hear nothing. My husband mentioned that it also sounds like a pager on vibrate mode.
 
  #9  
Old 11-21-06, 07:00 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Buzz

I suspect it to be only in one zone & only under certain conditions such as when the zone valve first opens. It is likely you have a heat pipe rubbing against wood somewhere & once that pipe gets hot & expands fully, the noise stops.
I have the same thing in one of my zones but it hasn't bothered me enough to fix it, yet.
 
  #10  
Old 11-22-06, 04:14 AM
N
Member
Thread Starter
Join Date: Jul 2005
Location: NJ
Posts: 261
Upvotes: 0
Received 0 Upvotes on 0 Posts
We heard it again last night. This time, it buzzed for a second or two, then buzzed again for a second or two. However, it stopped before the boiler shut down. My husband heard it too. He said that it sounded like vibration. I love for it to be caused by vibration/pipe rubbing. How can I be sure? Thanks.
 
  #11  
Old 11-22-06, 01:01 PM
X
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes on 0 Posts
No expert here, but a question for them. Could this be a faulty relay?
 
  #12  
Old 11-22-06, 02:43 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Originally Posted by xiphias
No expert here, but a question for them. Could this be a faulty relay?
Yeah, could be "chattering" or something!

I would say to look around and wiggle some pipes and see if you can make it stop or start. I'm thinkin' keep an eye (or ear, as it were) on it and see what happens... keep looking and try to "catch it in the act" if you can. Sometimes just lightly pushing on the pipes can cause a vibration to re-appear. I'm with Grady on this...

One time I almost replaced a well pump... until I discovered the two pipes that were vibrating together. Sounded just like a bad bearing in the motor.

I have had burner couplings go bad and make funny noises intermittently though...

I'm still wondering though, your description at one point made it sound like the burner might be "short cycling" ... How long is the burner running on a typical cycle ? ?

This is the kind of thing that could possibly be nothing, or it could be something. Vague enough for ya ???

-
 
  #13  
Old 11-23-06, 03:37 AM
N
Member
Thread Starter
Join Date: Jul 2005
Location: NJ
Posts: 261
Upvotes: 0
Received 0 Upvotes on 0 Posts
I will try and catch it in the act (don't know how successful I will be).

The burner can run between 1 and little over 2 minutes. Sometimes the burner will kick on, run a couple of minutes, and stop. Then, a few seconds to minutes later, it will repeat the cycle. This happens when it is cold outside.
 

Last edited by Novice134; 11-23-06 at 03:49 AM.
  #14  
Old 11-23-06, 09:14 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Originally Posted by Novice134
The burner can run between 1 and little over 2 minutes. Sometimes the burner will kick on, run a couple of minutes, and stop. Then, a few seconds to minutes later, it will repeat the cycle. This happens when it is cold outside.
That description sounds to me as though you may have a problem that should be looked at. One minute is an awfully short time for a burner to run, and then you say it stops briefly and starts again ? No, that ain't right.

If you were to tell me that in the dead of winter, on the coldest night, the burner ran for 4 minutes, and then in 4 minutes came back on again, I might say OK... but it's really not cold enough for the kind of behaviour you are describing yet. Unless you are in Alaska or Siberia... yer not, right ?
 
  #15  
Old 12-07-06, 01:47 PM
N
Member
Thread Starter
Join Date: Jul 2005
Location: NJ
Posts: 261
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sorry it took so long to respond. My husband replaced a couple of broken plastic pipe brackets with copper ones. As a result, the buzzing had transferred occasionally to the bedroom. He then replaced more broken plastic brackets with copper ones. I am now on wait mode to see if we will hear the buzz again.

What do you think needs to be done with the burner if it is running too often? The frequency of the burner running varies a lot. My husband thinks I have monitored it on a cold night (though we don't live in Alaska or Siberia).
 
  #16  
Old 12-07-06, 02:05 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

What do you think needs to be done with the burner if it is running too often? The frequency of the burner running varies a lot. My husband thinks I have monitored it on a cold night (though we don't live in Alaska or Siberia).

Dont know what tstat you have there . But the run time on a unit is set by the tstat Check the anticipator
 
  #17  
Old 01-17-07, 04:26 AM
N
Member
Thread Starter
Join Date: Jul 2005
Location: NJ
Posts: 261
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sorry about the late post. The holidays took over.

Ed, I don't know what an anticipator is. Where will it be located?

BTW, lately, I have not heard the buzzing noise. I don't know if replacing the broken brackets was the recent why the buzzing noise stopped.
 
  #18  
Old 01-17-07, 06:25 PM
T
Member
Join Date: Jan 2007
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
boiler over fired or high limit set too low

Originally Posted by Novice134 View Post
Lately, during the early mornings when the house is quiet, I sometimes hear buzzing sound that I believe is related to the boiler. Our bedroom is on the second floor opposite side of the house from the boiler in the basement. But, when the boiler starts up, I can hear it. Occasionally, a few seconds after the boiler starts up, a buzzing sound can be heard. The sound lasts a few seconds and stops when the boiler shuts down. To me, the buzz sounds like electricity, kind of like a bug getting zapped. My husband heard it once and said it sounded like buzzing. This does not happen all the time. I don't hear this sound during the day. What can it be? Can it be vibration? What can be wrong with the boiler? Thanks.
if the boiler only runs for a couple of minutes it could be over fired on the high limit is set too low.
 
 