Boiler pressure
Old 12-02-06, 04:46 AM
B
Cool Boiler pressure
Can anyone help?
I have a combo oil fired and wood burning furnance, approx 27 years old, I notice that pressure is constantly building past 30#. I always need to open the relief valve to let some pressure out. Question is on the expansion tank behind the boiler when I press in the pin in the valve, should water or air come out? I suspect that this is my problem.
Thanks
Rick
Old 12-02-06, 12:30 PM
Grady's Avatar
Received 41 Upvotes on 39 Posts
Exp. Tank
You should get air out of the schrader. If you get water, the tank needs to be replaced.
Old 12-02-06, 12:40 PM
NJT's Avatar
NJT
NJT is offline
Received 8 Upvotes on 6 Posts
Could there be an issue with the PRV also ? If it were just the tank waterlogged, I wouldn't think you would need to constantly be letting out pressure. Sounds like you might have two problems ?
Old 12-03-06, 03:42 AM
B
pressure
Pressure relief valve I did change at first, since I thought that was faulty. Come to find out my expansion tank was water logged. ( Boy was that sucker heavy). Also, changed the water relief valve ( valve that controls water coming into the boiler) which was loaded with crud. Now I am good as new, got the wood fire going in the furnance and maintaining constant pressure at 15-18 lbs.
Thanks for your response.
Rick
Old 12-03-06, 06:58 AM
Grady's Avatar
Thumbs up Good Work
Those tanks can be surprisingly heavy & really fool you if you're not prepared. Glad you got it fixed.