Burnham Boiler Intermittent

system fires up ok but only runs for 1 min. before shutting down.
I am thinking it could be circulator pump and high limit switch shuts system down?
The pump is a B&G NRF22 - it is not hot to the touch -
 
  #2  
Old 12-04-06, 09:34 PM
M
Member
Join Date: Feb 2005
Location: Southern Illinois
Posts: 28
Upvotes: 0
Received 0 Upvotes on 0 Posts
Are you using zone valves or a circulator pump for each zone? If no zone valve, does the thermostat connect to the pump or the relay/aquastat first? How many zones do you have?

It sounds like you are running a single pump and that the zone valves or relay are too blame, but more info including probably a couple of trouble shoot tests are needed to narrow it down.
 
  #3  
Old 12-05-06, 05:42 AM
T
Member
Thread Starter
Join Date: Dec 2006
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
burnham

Originally Posted by M. Under Bone View Post
Are you using zone valves or a circulator pump for each zone? If no zone valve, does the thermostat connect to the pump or the relay/aquastat first? How many zones do you have?

It sounds like you are running a single pump and that the zone valves or relay are too blame, but more info including probably a couple of trouble shoot tests are needed to narrow it down.
Only one pump and no zone valves
this is one loop system to small apt.
 
  #4  
Old 12-05-06, 03:53 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Can you tell if the circulator is running ?

Do the pipes get hot at any distance from the circulator ?

When you say it goes for a minute and shuts down, it's not tripping the control on the burner, right ? I mean, you don't need to push the reset button to get it to fire again, do you ? If that's the case, then you have a problem with the burner itself.

When it shuts off, what temperature is showing on the boiler gauge ? Is it actually hitting high limit (appx 160-180*F) ?
 
  #5  
Old 12-05-06, 10:23 PM
T
Member
Thread Starter
Join Date: Dec 2006
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by NJ Trooper View Post
Can you tell if the circulator is running ?

Do the pipes get hot at any distance from the circulator ?

When you say it goes for a minute and shuts down, it's not tripping the control on the burner, right ? I mean, you don't need to push the reset button to get it to fire again, do you ? If that's the case, then you have a problem with the burner itself.

When it shuts off, what temperature is showing on the boiler gauge ? Is it actually hitting high limit (appx 160-180*F) ?
it seems that the thermostat was the problem - not calling properly - also there was some air in system -
What is the high limit proper setting? the dial shows up to 240F?
 
  #6  
Old 12-06-06, 07:24 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Usually 180*F ... sometimes less, usually not more for a baseboard system.
 
  #7  
Old 04-12-07, 09:00 PM
S
Member
Join Date: Apr 2007
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
if the system fireups and everything is in place , could be the flame sensor.

if its a honeywell intermittent control board .

If you dont have a spare flame sensor try to clean it with some sand paper.
 
 