Baxi 80E no pilot light - no warnings either

Had a few problems with this crap boiler,

Today the pilot light won't ignite, there are no warnings, the power light is on but the yellow light won't come on to indicate the pilot light is running, i can hear a fan working .
i have pressed the button inisde the boiler on the left along the copper pipe (thinking it is a reset ) or i could be pressing nothing.

any ideas - its a bit cold

tried turning to reset also and turning it off for a few minutes
 
Sponsored Links
  #2  
Old 12-30-06, 07:56 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,230
Received 22 Votes on 20 Posts
No pilot

Most burners must establish draft before they will light. Make sure the vent pipe is clear & not clogged. What ignition control is on the boiler?
 
  #3  
Old 01-01-07, 10:12 AM
HVAC-EMT's Avatar
Member
Join Date: Dec 2006
Location: The Berkshires
Posts: 165
Received 0 Votes on 0 Posts
Cool Wall mounted boiler

I googled it and found lots of people have had problems with them. If the power venter is running, but the pilot light wont come on (this has an intermittant pilot instead of a standing pilot I assume), then the fan switch probbably isn't proving. Go outside to where it vents and see is it is blowing or not, and also check for obstructions. This is the first step.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: