hot pipe - cold radiator


  #1  
Old 12-30-06, 07:45 PM
E
Member
Thread Starter
Join Date: Dec 2006
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
hot pipe - cold radiator

i have steam heat and have a cold radiator on the second floor. the pipe leading to this radiator is hot on the first floor so it would seem the steam is getting to (or close to) the radiator but the whole radiator, including the shutoff valve are cold on the second floor. the vent valve (new and wide open) does some hissing which leads me to believe that the steam is getting close and that air can pass through, but no steam is entering the radiator. the radiaitor pitch is half a bubble back toward the pipe (single pipe steam). the rest of the radiators in the system are operating fine. any thoughts?
 
  #2  
Old 12-30-06, 08:01 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Cold Radiator

There are vents made for second floor radiators. They have a larger opening for faster venting. For a quick test you could remove the vent. When the rad gets hot about 1/2 way across or so, get that vent back in quick. You don't want live steam coming out. All this will tell you is if the rad is getting steam & you may need a larger vent.
 
  #3  
Old 12-30-06, 09:02 PM
E
Member
Thread Starter
Join Date: Dec 2006
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
i'll give this a try

thanks grady - let me say first that all the other radiators in the house have the same vents. that said, i'll post the results after trying your suggestion. thanks.
 
  #4  
Old 12-30-06, 09:25 PM
HVAC-EMT's Avatar
Member
Join Date: Dec 2006
Location: The Berkshires
Posts: 152
Upvotes: 0
Received 0 Upvotes on 0 Posts
Smile Check the radiator valve.

How old is the shut-off valve on the radiator? I've seen this type of thing before, and found the valve gasket had fallen off and landed on the seat. The flow was so low that the steam condensed before it got to the radiator. Replacing the valve did the trick. You did make sure the valve is fully open, right? Also, some vents, such as Vari-vents, are adjustable. Good luck!
 
  #5  
Old 12-30-06, 10:12 PM
E
Member
Thread Starter
Join Date: Dec 2006
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
replace shutoff valve

i'm inclined to agree that this may be my best course, though i'll follow Grady's advice first. the shutoff valve is fully open and the vent is fully open (the adjustable type). i have no idea how old the valve is - i bought the home two years ago. how difficult is it to replace the shutoff valve? i have no experience with this - steam heat is new to me.
 
  #6  
Old 12-30-06, 11:12 PM
HVAC-EMT's Avatar
Member
Join Date: Dec 2006
Location: The Berkshires
Posts: 152
Upvotes: 0
Received 0 Upvotes on 0 Posts
Red face Replacing shut-off valve

They can sometimes be quite difficult to replace, and sometimes quite easy. It is hard to tell till you try it. Materials needed: REPLACEMENT VALVE - make sure it is the same size and type; TEFLON TAPE - 3/4" roll is prefferable, but 1/2" will work too; & SOFT-SET PIPE DOPE - not neccesary, but wouldn't hurt. Tools I reccomend having on hand before trying it: PIPE WRENCHES (2 minimum) - the bigger the better, I say (Ridgid brand is preferred, but can be pricey if you don't use them on a regular basis...24" and/or 36") if you know someone you can borrow them from, you can save some $$...I think some places rent them too; MAPP OR PROPANE TORCH - the hotter the better; SAWZALL - A few 6" fine toothed metal blades too; and a INTERNAL WRENCH -for removing the union that attaches to the radiator. I will continue tomorrow with instructions. My wife say's it's past time for me to come to bed.
 
  #7  
Old 12-31-06, 04:12 AM
X
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes on 0 Posts
There's a great book by Dan Holohan called "We Got Steam Heat" that you can google and buy. Excellent homeowner reference.
 
  #8  
Old 12-31-06, 06:23 AM
HVAC-EMT's Avatar
Member
Join Date: Dec 2006
Location: The Berkshires
Posts: 152
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thumbs up Dan Holohan

Originally Posted by xiphias View Post
There's a great book by Dan Holohan called "We Got Steam Heat" that you can google and buy. Excellent homeowner reference.
Dan is the man! Check out www.HeatingHelp.com It is Dan Holohan's website. I've seen him at seminars and learned a lot. He is a great speaker and author and the "Guru" of steam heat. All his books are great. It usually costs $200 or so to go to his seminars, but it is worth every penny! I just checked, and he has a class in Somerville, MA (near Boston) on January 16th, and Warwick, RI on January 17th from 5pm to 8:30pm for only $129 including the buffet and book discounts! They always sell out, so if you want tickets, order them now. The next seminar after that looks like it is in Piscataway, NJ on March 24th from 8am-3pm at a cost of $140-$200 depending on when you buy the tickets, and wheather you take the RSES test. Price of $140 is only good today, then on 1/1/07 it goes up to $160.
http://www.heatinghelp.com/seminars.cfm
 
  #9  
Old 12-31-06, 07:08 AM
HVAC-EMT's Avatar
Member
Join Date: Dec 2006
Location: The Berkshires
Posts: 152
Upvotes: 0
Received 0 Upvotes on 0 Posts
Talking Replacing radiator valve

Ok, went off on a tangent, now I am back. I reccomend doing this on a weekday in the morning, so that if anything goes wrong, you can call your service company to help you out, and it won't cost you time and a half or double time. First thing you need to do to replace the radiator valve is turn the heat off, allow the radiator to cool (which I'm sure yours is already) & close the radiator valve. Next, disconnect the union between the radiator and the valve. I assume you know how to do that, but just in case, when you are over the valve with the radiator in front of you, turn the nut dovn and to the right (clockwise). It wouldn't be a bad idea to have another person there to help make sure the radiator doesn't fall over (I've only dropped one once, but hey, ya never know). Once you have the union apart, with help (especially if it is a big radiator), move the radiator to the side. Be careful not to scratch the floors. If you want to inspect the inside of the valve (does it really need to be replaced??), you can open it back up (just don't have your face in the way when you open it in case there is still pressure on the system) and look to see if the seat is ok or not. If it has fallen apart or off, I would just replace the whole thing. Assuming you have an angle valve, put one pipe wrench on the bottom pipe with the handle to the right and the jaw opening towards you. Put the second pipe wrench with the handle to the right and the jaw facing away from you on the knuckle of the radiator valve with the handle a little closer to you than the other wrench. Pull them towards each other. This is where bigger wrench = better. Don't hurt yourself trying to get it off. If it won't budge, there are a few tricks you can use. There are relief cuts you can make on the valve (take the sawzall and cut the knuckle of the valve parrallel to the pipe without cutting the pipe while getting as close to the threads as possible. This will weaken the brass threads and make it crack when you try again). Another option is, you can take the torch and heat up the valve till it is extremely hot and try again. This will loosten up the dope and threads making it turn easier. **Just be sure that if you use this method, you are very careful not to light your house on fire, bubble up the paint on the wall, burn your wall paper, or burn you!** You may also want to take an adjustable wrench and screw driver and remove the handle, nut, and valve stem first. The rubber part inside makes smoke when it burns. Once you have the valve off, you can take a wire brush or fitting brush (3/4" works good) and clean up the threads on the pipe. Next, if you are looking down at the pipe, wrap teflon tape on the threads going around it clockwise with the tape coming off the bottom of the roll. Put at least 4 wraps (6 would be better) on the threads keeping the tape taught. If you put a lot of teflon on, pipe dope isn't always neccesary. put dope over the tape in a clockwise motion (so as not to take the tape off). Turn the new valve onto the threads till it is tight (don't over tighten it or under tighten it) and pointing in the same direction the old one was. If you want to, you can now close the new valve (if it already wasn't) and turn the heat back on. I will be back later to let you know how to replace the radiator portion (if it needs it).
 
  #10  
Old 01-01-07, 06:24 PM
E
Member
Thread Starter
Join Date: Dec 2006
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Replacing radiator valve

hvac-emt,

Thanks for your instructions. i think i can folllow these without too much difficulty (fingers crossed) and hopefully the person who last had it apart was good enough to use teflon and dope. i do have a question, though. you say to look inside the valve to determine if it needs replacing. i've never looked inside one of these - will it be obvious to me if it needs replacing? what, exactly, am i looking for?
 
  #11  
Old 01-02-07, 12:22 AM
HVAC-EMT's Avatar
Member
Join Date: Dec 2006
Location: The Berkshires
Posts: 152
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question valve

You will be looking for the gasket that attaches to the valve stem. It could have fallen and landed on the valve seat. Should be pretty obvious. It's been a while since I've done this. It could also be possible that the seat has totally disappeared (down the pipe?) Did you already try the air vent thing? Insulating the pipe going to the radiator should also help get the steam there quicker.
 
  #12  
Old 01-02-07, 07:23 PM
E
Member
Thread Starter
Join Date: Dec 2006
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
valve

hvac-emt,

thanks for all this information. i'll not get to this until this weekend and will be sure to get back to you with what i find. i'll also be trying grady's suggestion...first. if you think of anything else between now and this weekend, please share. yuo've been very informative - thanks very much.
 
  #13  
Old 01-06-07, 05:57 PM
E
Member
Thread Starter
Join Date: Dec 2006
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
results

hvac-emt,

well i took a different tack in hopes of finding something before dis-assmbling anything. on the advice of a friend, i closed all the other valves in the system. two would not close, so i went with three radiators open. he mentioned that it would be a good way to isolate the radiator to be absoluely sure it would not take steam. i cranked up the heat and what happens is this - the steam enters the radiator but stays along the bottom middle pipe. it makes its way across the bottom of the radiator and up to the vent, thereby heating/closing off the vent before the radiator can heat up. the rest of the radiator stayed dead cold except for the very bottom center cross-section. am i making sense? does this sound like anything you've seen?
 
  #14  
Old 01-06-07, 06:05 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Radiator

I'm guessing the rad is clogged with rust. Try taking a RUBBER hammer & beating on the sections in hopes of breaking the rust loose.
 
  #15  
Old 01-06-07, 08:38 PM
E
Member
Thread Starter
Join Date: Dec 2006
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Radiator

thanks grady - i'll give it a shot. what odds do you give me that it works?
 
  #16  
Old 01-07-07, 01:23 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Odds?

Long, at best. Maybe KField has some ideas. I'll ask him to look at this thread.
 
  #17  
Old 01-07-07, 04:08 PM
KField's Avatar
Member
Join Date: Dec 2002
Location: Easton, PA
Posts: 3,015
Upvotes: 0
Received 0 Upvotes on 0 Posts
Something isn't quite adding up. My initial suggestion would be, take the valve apart and see it everything is in tact. If it is, which sounds likely, close it and disconnect the radiator from the valve at the union. Then move it slightly and look into it with a flashlight. Each piece of information gained is like a fork in the road. If the valve is damaged inside, remove the disc and make sure there is no other debris inside and try the system again. Part of what you say sounds like steam is traveling at a high velocity through the radiator. That could be caused by some sort of restriction. If the valve is functional, you can remove the radiator and not have a problem with heat in the rest of the house. If you remove the radiator, you can open the valve carefully with the outlet pointed into a bucket and see if you get a full flow or just a dribble of steam. Post back with any new information.

Ken
 
  #18  
Old 01-08-07, 05:56 AM
E
Member
Thread Starter
Join Date: Dec 2006
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
valve

KField,

thanks for this and it piggy-backs onto what hvac-emt has indicated. you both suspect something with the valve. i'll follow the experts and post back. weekends offer me the only opportunity, though, so i'll be a while getting back to you. many thanks.
 
 