I have an OLD steam boiler (Pennsylvania Furnance & Iron Co, Boiler # 3023 SA, Serial # 9-38062-16). It had been working fine until the other day when there was no heat. I checked the pilot and it was lit so I disconnected the thermostat. I have two wires (R & W). When I connect them together the boiler kicks on with no problem. But when I connected the wires to a new thermostat (Honeywell CT87K), the blower would not come on even with the temp cranked all the way up. The temp is now stuck at 62 even with the T-stat set to 70. I even bought another CT87K and tried that and had the same problem.

Any ideas?
 
  #2  
Old 01-23-07, 06:54 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,673
Received 40 Upvotes on 38 Posts
Wires

Do you know the voltage on those two wires? That thermostat is only good for 24 volt applications.
 
  #3  
Old 01-24-07, 04:54 AM
HVACGuy's Avatar
Member
Join Date: Jan 2007
Location: Upstate New York
Posts: 132
Upvotes: 0
Received 0 Upvotes on 0 Posts
Cool

What did you mean that the blower wont come on? You said that it has a pilot, so it's a gas boiler correct?
Is it a conversion type burner, with a draft inducer fan?
If so, I'll assume that it has a 24 volt control circuit. The CT87K is the regular, round heat-only stat. Did you install the new sub-base as well?
 
  #4  
Old 01-24-07, 09:51 AM
M
Member
Thread Starter
Join Date: May 2006
Location: Massachusetts
Posts: 56
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Grady. That's my problem. It's a 750 mv application so I have the wrong thermostat.
 
 