Thermostat problem?
#1
Member
Thread Starter
Join Date: May 2006
Location: Massachusetts
Posts: 56
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thermostat problem?
I have an OLD steam boiler (Pennsylvania Furnance & Iron Co, Boiler # 3023 SA, Serial # 9-38062-16). It had been working fine until the other day when there was no heat. I checked the pilot and it was lit so I disconnected the thermostat. I have two wires (R & W). When I connect them together the boiler kicks on with no problem. But when I connected the wires to a new thermostat (Honeywell CT87K), the blower would not come on even with the temp cranked all the way up. The temp is now stuck at 62 even with the T-stat set to 70. I even bought another CT87K and tried that and had the same problem.
Any ideas?
Any ideas?
#3

What did you mean that the blower wont come on? You said that it has a pilot, so it's a gas boiler correct?
Is it a conversion type burner, with a draft inducer fan?
If so, I'll assume that it has a 24 volt control circuit. The CT87K is the regular, round heat-only stat. Did you install the new sub-base as well?
Is it a conversion type burner, with a draft inducer fan?
If so, I'll assume that it has a 24 volt control circuit. The CT87K is the regular, round heat-only stat. Did you install the new sub-base as well?