boiler help needed

i have a 'CROWN' gas boiler (furnace).[ it is the type that runs hot water around the house in copper pipes ] the pilot only stays on for about 35 min. ive replaced the thermocouple, thermal cuttof resistor, the thermostat has been recently replaced. can anyone offer any suggestions on what to look for??
 

Last edited by towncarblue; 01-25-07 at 05:46 PM.
  #2  
Old 01-25-07, 06:17 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

Is it a standing pilot lit all the time?? If so did you clean the pilot light orifice and the venturi around it ??? Dont use a pin in the orifice there. Does the tip of the T/C get red?
 
  #3  
Old 01-25-07, 06:33 PM
T
Member
Thread Starter
Join Date: Jan 2007
Location: bronx ny
Posts: 68
Received 0 Upvotes on 0 Posts
it is a pilot that is supposed to be lit all the time

what is the pilot light orifice? is it the housing for the trermocouple??

what is the best way to clean it??

the flame for the pilot starts off yellowish , then it gets blue

the tip of the thermocuple get orange-reddish
 
 