replace circulating pump on boiler system
#2
Add water back to the boiler, to maintain 12-15 psi, and then bleed the radiators with the pump going. You may want to simply over-pressure the boiler initially by adding about 25 psi worth and then bleed the radiators. When you do, the pressure will drop. If it doesn't drop back to 12-15 psi, then drain some water out of the boiler drain.
If your boiler maintained that 12-15 psi on auto-fill, then you shouldn't have to monkey with that at all. But new autofills have a nice feature where there is a lever on them that allow you to override the auto-fill regulator to dump more water, quickly into the boiler.
If your boiler maintained that 12-15 psi on auto-fill, then you shouldn't have to monkey with that at all. But new autofills have a nice feature where there is a lever on them that allow you to override the auto-fill regulator to dump more water, quickly into the boiler.