Air Scoop Location
#1
Member
Thread Starter
Join Date: Jun 2007
Location: North of Boston, MA
Posts: 29
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Air Scoop Location
Hello,
I'm doing a tight-space boiler install where I have very little space to work. The boiler is a burnham V8 series boiler. I am planning on using a conventional Taco air scoop with the tank and air eliminator below and above.
According to the burnham instructions, they recommend 18" of pipe between the boiler outlet and the scoop, presumably to settle down the water before it goes through the scoop. I assume that this means "horizontal" pipe, after the elbow on the vertical rise. Does this also mean, there can't be elbows in between? For instance, can I use (2) 9" pipes with a 90 degree elbow in between? If not, it seems I have to expand the space a little.
Thanks for the info in advance.
I'm doing a tight-space boiler install where I have very little space to work. The boiler is a burnham V8 series boiler. I am planning on using a conventional Taco air scoop with the tank and air eliminator below and above.
According to the burnham instructions, they recommend 18" of pipe between the boiler outlet and the scoop, presumably to settle down the water before it goes through the scoop. I assume that this means "horizontal" pipe, after the elbow on the vertical rise. Does this also mean, there can't be elbows in between? For instance, can I use (2) 9" pipes with a 90 degree elbow in between? If not, it seems I have to expand the space a little.
Thanks for the info in advance.
#2
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You need 18" of straight horizontal pipe leading into that air scoop. If you're tight on space, use a Spirovent, Taco 4900, or Honeywell air eliminator instead. Cost a bit more, but don't have the straight pipe requirement and generally work better to boot.
The straight pipe requirement is as you suspect to allow the water to settle (actually, allow the bubbles to rise).
The straight pipe requirement is as you suspect to allow the water to settle (actually, allow the bubbles to rise).
#5
Member
Join Date: Aug 2006
Location: usa
Posts: 839
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Make sure you pump away from the scoop and tank, having the PNPC at that point will help purge trapped gasses from the boiler water so the scoop can do its job better.