New Yorker boiler wont stay running.


  #1  
Old 06-17-07, 09:27 AM
W
Member
Thread Starter
Join Date: Jun 2007
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Angry New Yorker boiler wont stay running.

I keep having to reset this boiler on the honeywell r8184g control, it fires back up and then sometimes after about 10 secs i can hear the spark stop sparking inside but the flame is still there, any help would be nice ty. by the way the burner is a carlin, and it was just cleaned.
 
  #2  
Old 06-17-07, 02:38 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Burner shuts down

If it was cleaned professionally, call the servicer back.
 
  #3  
Old 06-17-07, 07:31 PM
hexonx's Avatar
Member
Join Date: Mar 2007
Location: 120 klicks from NYC
Posts: 66
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thumbs down Just cleaned? Shame on them.

As Grady said call them back. Also you they should have adjusted the electrodes after changing the nozzle and fuel filter. The fuel pump should have been bled and the pressure adjusted accordingly. If this is a service contract they owe you a combustion analysis printout. If the spark is not sparking, sounds like a quick replacement job without any adjustments. I maybe wrong but I am speaking from experience.
 
 