Tankless Loop / Flow Regulator

Hi,

I'm installing an Burnham V8 series boiler with a front tankless loop. In the manual, as part of the install, it requires a mixing valve, and a flow regulator. I have purchased a Taco 5000 series mixing valve, but I'm not quite sure what I should buy for the flow regulator. Since it's in the manual, I assume it's required? I understand why it's there, but I'm not quite sure what will do the job. I prefer something that will sweat, and is 3/4".

I am referring to page 39 of this pdf: http://www.usboilerco.com/pdfs/CurrentPDFfiles/V8_I&O.pdf

Thanks
 
  #2  
Old 07-09-07, 08:31 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,644
Likes: 0
Received 42 Likes on 35 Posts
The flow restricor is required if the flow through the coil is too great. The mixing valve is required but the flow restrictor may not be. If needed the flow restrictor must match the coil flow rate. The restrictor keeps from overdrawing the coil to verify you do not run out of hot water.The distributor where the boiler was purchased can assist you with the brand they carry. The control settings are also important. Set the high and low at least 20f apart. For example 150 low and 170f high. Do not exceed 190 low and 210 high. The diff should be as high as it goes which is 25f
 
 