Oil Burner Rumbles at turn off
#1
Member
Thread Starter
Join Date: Sep 2007
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts

I have an HB Smith boiler with a Carlin burner- Over the last couple of weeks, the furnace is making a rumbling sound after the burner turns off. It sounds a lot like the rumbling you would get on startup when the burner does not start right away and there is unburned oil in the burn chamber.
The burner is starting fine just not turning off the way it should. Any ideas of what to look for?
Thanks!
The burner is starting fine just not turning off the way it should. Any ideas of what to look for?
Thanks!
#4
Member
Thread Starter
Join Date: Sep 2007
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Rumble Fixed
I pulled the burner assembly this weekend and found quite a mess- The flame retention ring was loaded with carbon and there was lots of soot-
I cleaned everything up and replaced the nozzle with the same nozzle type. Put things back together and fired it up-
Looked in the inspection hole and holy smoke, looked like it was burning way to rich- So I adjusted the air band and got a nice looking burn. Not sure why the tech closed down the air band so much when it was serviced in March of 2006.
Anyhow, things seem stable now. It still starts good and I have no rumble at turn off.
I guess I probably need to get someone in to clean the heat exchanger. With how rich it was burning and the amount of soot/carbon on the burner assembly, I can only guess what the heat exchanger looks like.
Thanks for all comments, Jim
I cleaned everything up and replaced the nozzle with the same nozzle type. Put things back together and fired it up-
Looked in the inspection hole and holy smoke, looked like it was burning way to rich- So I adjusted the air band and got a nice looking burn. Not sure why the tech closed down the air band so much when it was serviced in March of 2006.
Anyhow, things seem stable now. It still starts good and I have no rumble at turn off.
I guess I probably need to get someone in to clean the heat exchanger. With how rich it was burning and the amount of soot/carbon on the burner assembly, I can only guess what the heat exchanger looks like.
Thanks for all comments, Jim
#5
Member
Join Date: Aug 2006
Location: usa
Posts: 839
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The combustion should be checked at a minimum by measuring the CO2 level in the flue gases, judging the flame by eye won't cut it. You could be on the wrong side of the curve and generating a lot of carbon monoxide, or the unit could be set too close to be reliably stable. Just my opinion, FWIW.
Pete
Pete
#6
Member
Join Date: Aug 2006
Location: usa
Posts: 839
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Another thing to watch for; assuming the burner was set right a few years back, the carbon build up could be caused by poor atomization of the oil at the nozzle.. Could be caused by low pump pressure? Clogged strainer? Just a few guesses. You should have a pro check it before the heating season.