Wiring reset for Burnham Revolution
#1
Member
Thread Starter
Join Date: Oct 2007
Location: USA
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wiring reset for Burnham Revolution
Greetings. I have a Burnham Revolution gas-fired boiler plumbed to converted steam radiators; circulator-zoned with two zones. Currently uses a Taco 2-zone switching relay to operate the boiler and the circulators. I'd like to add more sophisticated control-- e.g. outdoor reset, etc. I'm looking at something like the Tekmar 336/420 combination.
My question is how to wire control of the boiler. Most of the reset controllers indicate that they should be wired to the T-T terminals of the boiler control. Seems easy enough, but...
The Revolution uses an L8148 aquastat which manages the burner and an internal boiler circulator. Closing T-T energizes the boiler circulator and the L8148 cycles the burner off the high limit.
So just wiring a reset controller to T-T isn't going to do the right thing. It seems like the reset controller replaces some of the L8148 functionality, but there does not appear to be any documented way to integrate external reset control.
Looking at the wiring diagrams, I think I see how I could jerry-rig things to work, but that clearly isn't the right answer.
I've looked at all of the Burhman installation instructions, but they don't discuss reset controls. What am I missing here? Surely there's a "proper" way to hook this up...
Thanks for any help.
-Chris
My question is how to wire control of the boiler. Most of the reset controllers indicate that they should be wired to the T-T terminals of the boiler control. Seems easy enough, but...
The Revolution uses an L8148 aquastat which manages the burner and an internal boiler circulator. Closing T-T energizes the boiler circulator and the L8148 cycles the burner off the high limit.
So just wiring a reset controller to T-T isn't going to do the right thing. It seems like the reset controller replaces some of the L8148 functionality, but there does not appear to be any documented way to integrate external reset control.
Looking at the wiring diagrams, I think I see how I could jerry-rig things to work, but that clearly isn't the right answer.
I've looked at all of the Burhman installation instructions, but they don't discuss reset controls. What am I missing here? Surely there's a "proper" way to hook this up...
Thanks for any help.
-Chris
#2
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Off the top of my head and without looking at any diagrams I think that the reset controller could be wired in series with the existing two-zone relay and the T-T terminals on the L8148.
#3
Member
Thread Starter
Join Date: Oct 2007
Location: USA
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the reply, furd.
My concern is about the internal boiler circulator: the Revolution has an internal loop which mixes boiler water with return water. If the reset breaks the T-T connection, this circulator will shut down too.
I've been assuming that the "right" thing would be to shut down just the burner and leave the boiler circulator running to try an capture as much heat from the boiler as possible.
-Chris
My concern is about the internal boiler circulator: the Revolution has an internal loop which mixes boiler water with return water. If the reset breaks the T-T connection, this circulator will shut down too.
I've been assuming that the "right" thing would be to shut down just the burner and leave the boiler circulator running to try an capture as much heat from the boiler as possible.
-Chris
#4
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
T-t
With an 8148, you need to remove the circulator from the aquastat's control. It can be wired thru a switching relay to energize whenever any zone is calling. If the zone relay has X terminals, they should provide closure for the switching relay.
Something here may help:
http://www.taco-hvac.com/uploads/Fil...ry/100-9.0.pdf
Something here may help:
http://www.taco-hvac.com/uploads/Fil...ry/100-9.0.pdf
#5
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hey y'all. Happy fall.
I have this setup. Revolution with a tekmar 260 and a Taco SR-503. There is a simple trick to wiring this setup that I received from Burnham, which is on another computer. I'll see if I can post it tomorrow.
The upshot is that the internal circ and aquastat need to do their own thing in order to provide the right circ speed and thus internal temps for boiler protection.
I have this setup. Revolution with a tekmar 260 and a Taco SR-503. There is a simple trick to wiring this setup that I received from Burnham, which is on another computer. I'll see if I can post it tomorrow.
The upshot is that the internal circ and aquastat need to do their own thing in order to provide the right circ speed and thus internal temps for boiler protection.