Buderus GB142 and AM10 Temp Sensor Connections Very Unclear
#1
Member
Thread Starter
Join Date: Oct 2005
Location: Rhode Island
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Buderus GB142 and AM10 Temp Sensor Connections Very Unclear
Have the Buderus GB142/24 with AM10 Temp Sensor.
Have 2 zone valves controlled by 2 thermostats operating at 24 volts . Do we have to provide a relay to operate the on - off terminals of the AM-10
It seems the AM-10 unit is not to supposed to see any voltage.
We can not find anything that is built into the GB142 to use this AM-10 with adding more items!
THanks
Have 2 zone valves controlled by 2 thermostats operating at 24 volts . Do we have to provide a relay to operate the on - off terminals of the AM-10
It seems the AM-10 unit is not to supposed to see any voltage.
We can not find anything that is built into the GB142 to use this AM-10 with adding more items!
THanks
#2
I just took a quick look at the AM10 supplement at Buderus.
It appears that if you are using a 4 wire zone valve with an isolated end switch, you won't need the extra relay, but if you are using the three wire type, then you need the relay to isolate the AM10 from the 24V transformer...
What ZVs are you using ?
It appears that if you are using a 4 wire zone valve with an isolated end switch, you won't need the extra relay, but if you are using the three wire type, then you need the relay to isolate the AM10 from the 24V transformer...
What ZVs are you using ?