W8665A to R8222 to TACO SR503
Need help wiring these three devices together.
W8655A - Honeywell thermostat
R8222B - Honeywell general purpose relay
SR503 - relay mounted on my boiler
I have a 2 zone heating system but I am using the W8655A as only 1 zone.
I have a separate A/C system that does not use the W8665A.
I have a red and white lead that originates from the SR503.
I do not know what number lead(1-6) from the R8222 connects to either of these leads from the SR503.
Then I have 3 leads from the W8665A (Red, White and Common(black) that connect to the R8222B - lead numbers 1-6
Thanks for any help
W8655A - Honeywell thermostat
R8222B - Honeywell general purpose relay
SR503 - relay mounted on my boiler
I have a 2 zone heating system but I am using the W8655A as only 1 zone.
I have a separate A/C system that does not use the W8665A.
I have a red and white lead that originates from the SR503.
I do not know what number lead(1-6) from the R8222 connects to either of these leads from the SR503.
Then I have 3 leads from the W8665A (Red, White and Common(black) that connect to the R8222B - lead numbers 1-6
Thanks for any help
#2
dj, it's unclear to me what you are trying to do ?
I'm thinking that it sounds as though you want to connect the wireless thermostat through the 8222 relay to control one of the zones on the 503 ? Is that correct ?
You need a source of 24VAC to power the 8665 ... do you have that available ?
I'm thinking that it sounds as though you want to connect the wireless thermostat through the 8222 relay to control one of the zones on the 503 ? Is that correct ?
You need a source of 24VAC to power the 8665 ... do you have that available ?
#3
Member
Thread Starter
Join Date: Nov 2007
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
nj,
Yes, I have a 24vac power source from the sr503. I tried directly wiring the red from the sr503 to the R, the white from the sr503 to the W, and the common from the sr503 to the C on the W8665A. But the power LED on the W8655a did not light up.
So I searched this forum and discovered that Jay111 recommended using the R8222 relay.
Don't know what else to do ...
Yes, I have a 24vac power source from the sr503. I tried directly wiring the red from the sr503 to the R, the white from the sr503 to the W, and the common from the sr503 to the C on the W8665A. But the power LED on the W8655a did not light up.
So I searched this forum and discovered that Jay111 recommended using the R8222 relay.
Don't know what else to do ...
#4
DJ,
Thanks for posting here, I was going to copy and move your PVT Msg here to share with others.
On the SR503, I pulled up a manual for it, but not being clear about it.. On the upper left hand side above the transformer, the manual says "24 VAC Power Source"
My question on that, is there two screws/tabs where may says 24v and com?
If yes, there is Hot and C, then wire the hot to R on the W8665, and C to C on W8665
Put the Red wire on #1, white wire on #3 of the relay.
Thanks for posting here, I was going to copy and move your PVT Msg here to share with others.
On the SR503, I pulled up a manual for it, but not being clear about it.. On the upper left hand side above the transformer, the manual says "24 VAC Power Source"
My question on that, is there two screws/tabs where may says 24v and com?
If yes, there is Hot and C, then wire the hot to R on the W8665, and C to C on W8665
Put the Red wire on #1, white wire on #3 of the relay.
#5
Member
Thread Starter
Join Date: Nov 2007
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Jay,
Yes, you are right...the 24vac hot and common tabs on the sr503 exist. I will try to wire the hot to R and the common to C.
Do I still need the R8222 relay ?
How do I wire it ?
Yes, you are right...the 24vac hot and common tabs on the sr503 exist. I will try to wire the hot to R and the common to C.
Do I still need the R8222 relay ?
How do I wire it ?
#6
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
SR503 common
I see no "common" terminal on the SR503. Where are you trying to pick up a common? If you don't have installation manuals for the controls, here are links to them:
http://customer.honeywell.com/honeyw...spx/R8222B1067
http://customer.honeywell.com/techli...0s/69-1630.pdf
http://www.taco-hvac.com/uploads/Fil...503102-083.pdf
I also don't understand why you need the 8222. Maybe because I don't fully understand what you are trying to do.
http://customer.honeywell.com/honeyw...spx/R8222B1067
http://customer.honeywell.com/techli...0s/69-1630.pdf
http://www.taco-hvac.com/uploads/Fil...503102-083.pdf
I also don't understand why you need the 8222. Maybe because I don't fully understand what you are trying to do.
#7
Yes, Put the W/Red wire from W8665 to one of the coil side of the R8222. White/c wire from W8665 to the other coil of R8222.
Then from the SR503.
Put the Red wire on #1, white wire on #3 of the relay.
Then from the SR503.
Put the Red wire on #1, white wire on #3 of the relay.
#8
DJ, Do you have a meter? Grady may be right, we may not need the relay.
#9
I think you do need the relay. I'm not sure whether or not the contacts on the 8665 are 'dry contacts', and I actually don't think they are. That stat appears to switch 24VAC to the three outputs, one for cool, one for heat, and one for fan. The installation of the 8665 shows relays...
In fact, I'd be hesitant to steal the power from the 503... why not just use a small external transformer ?
Using the 8222 relay will provide the dry contact required for the 503 ...
Look at it this way... it's cheap insurance, and it can't hurt. Don't use it and risk ruining a pretty expensive t'stat ! and/or the 503 too!
In fact, I'd be hesitant to steal the power from the 503... why not just use a small external transformer ?
Using the 8222 relay will provide the dry contact required for the 503 ...
Look at it this way... it's cheap insurance, and it can't hurt. Don't use it and risk ruining a pretty expensive t'stat ! and/or the 503 too!
#11
NJ is right... Keep the relay!
wire it up as I stated before. If you want me to draw it up, I can.
NJ, the 503 got it's own transformer, so should have plenty of power to run the 8665.
wire it up as I stated before. If you want me to draw it up, I can.
NJ, the 503 got it's own transformer, so should have plenty of power to run the 8665.
#12
I think so too... funny thing is, none of the install sheets on the website show any use of the "24 V POWER" terminals.
This one has diagrams of all the products:
Zone control wiring guide
I'm sure there is a way to wire it up without the relay, but without being able to handle the stuff and put a meter on it, etc, it's difficult to be certain over the internet!
#14
NJ,
Yeah, that's why I asked him to be sure if there is 24 and C on the 503, and he said yes.
#15
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
I'm hardheaded
Can somebody explain to me why this would not work: R from 503 to R on stat; common from 503 to C on stat; W from 503 to W on stat.
When R-W closes on stat during a call for heat, power goes back thru R to W on 503 causing X1-X2 (dry contacts) to close. The closure of X1-X2 closes T-T on the aquastat.
What am I missing?
When R-W closes on stat during a call for heat, power goes back thru R to W on 503 causing X1-X2 (dry contacts) to close. The closure of X1-X2 closes T-T on the aquastat.
What am I missing?
#16
Grady,
The way I see it on my end, W from the 8665 needs to go to a "load". (coil on the 8222 is a load)
Where on the 503's zone (say Zone1) goes to a thermostat. (A switch)
The way I see it on my end, W from the 8665 needs to go to a "load". (coil on the 8222 is a load)
Where on the 503's zone (say Zone1) goes to a thermostat. (A switch)
#18
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
503
Each of the pairs of zone terminals is an R & W (although not marked as such)
The C would be the Aux. 24v common.
I'd have to meter it to be positive but so I believe. I'd bet if you checked from 24v to one side of each pair you'd get nothing (same circuit) & from 24v to the other side, you'd get 24v.
The C would be the Aux. 24v common.
I'd have to meter it to be positive but so I believe. I'd bet if you checked from 24v to one side of each pair you'd get nothing (same circuit) & from 24v to the other side, you'd get 24v.
#19
I just drew out what Grady just said...
Yes, that would work, near as I can tell.
One of the ZONE terminals is internally wired to 24VAC HOT, or R ...
The other ZONE terminal goes to one side of the relay coil in the 503 for that particular zone, or W . The other side of that relay coil goes internally to 24VAC Neut...
So, if dj metered from the aux Common terminal to each of the ZONE inputs, one would be 24VAC, and that's the one to wire to the R on the stat...
The other one would go to W on the stat...
and the C goes to the C ...
that's what yer saying Grady ?
Yes, that would work, near as I can tell.
One of the ZONE terminals is internally wired to 24VAC HOT, or R ...
The other ZONE terminal goes to one side of the relay coil in the 503 for that particular zone, or W . The other side of that relay coil goes internally to 24VAC Neut...
So, if dj metered from the aux Common terminal to each of the ZONE inputs, one would be 24VAC, and that's the one to wire to the R on the stat...
The other one would go to W on the stat...
and the C goes to the C ...
that's what yer saying Grady ?
#22
Right... 3 wires total ...
First he should meter and label with a marker the R and W, if not already marked on the 503 ...
With 503 powered up, measure from the aux 24 common to each ZONE terminal. Label the one that reads 24 VAC as R.
Label the other as W.
R to R , W to W , C to C ...
First he should meter and label with a marker the R and W, if not already marked on the 503 ...
With 503 powered up, measure from the aux 24 common to each ZONE terminal. Label the one that reads 24 VAC as R.
Label the other as W.
R to R , W to W , C to C ...
#23
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Sounds too easy
Right... 3 wires total ...
First he should meter and label with a marker the R and W, if not already marked on the 503 ...
With 503 powered up, measure from the aux 24 common to each ZONE terminal. Label the one that reads 24 VAC as R.
Label the other as W.
R to R , W to W , C to C ...
First he should meter and label with a marker the R and W, if not already marked on the 503 ...
With 503 powered up, measure from the aux 24 common to each ZONE terminal. Label the one that reads 24 VAC as R.
Label the other as W.
R to R , W to W , C to C ...
#25
Member
Thread Starter
Join Date: Nov 2007
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I actually have a meter and when I first started to unravel this mystery I sent an email to the tech lead at TACO in order to find the common.
I then attached the meter to the common on the 503 and to the RED terminal (which is where my current wired t-stat's red is bolted). I read 24VAC on the RED and then just hooked the Red to the R on the W8665A, White to W and common to C on the W8665A. I thought this would work, but the power LED on the W8665A did not light up. The remote temperature unit(T8665A) was calling for heat and so when I saw the led on the 503 light up, I thought it was working. But then I reset the remote unit so it would not call for heat and expected the led on the 503 to turn off. But the led did not turn off on the 503.
So then I did not know what to do and that is when I started to look for help.
I then attached the meter to the common on the 503 and to the RED terminal (which is where my current wired t-stat's red is bolted). I read 24VAC on the RED and then just hooked the Red to the R on the W8665A, White to W and common to C on the W8665A. I thought this would work, but the power LED on the W8665A did not light up. The remote temperature unit(T8665A) was calling for heat and so when I saw the led on the 503 light up, I thought it was working. But then I reset the remote unit so it would not call for heat and expected the led on the 503 to turn off. But the led did not turn off on the 503.
So then I did not know what to do and that is when I started to look for help.
#27
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Just curious
Did you also check common to white?
I don't know why it wouldn't work. As far as I can tell, the only reason for the relay is to isolate the two transformers. That is the one supplying power to the W8665 & the one on the aquastat. Since the X1 & X2 terminals on the 503 are dry contacts, they become the isolation. The only thing I can think of is maybe the transformer on the 503 may not be heavy enough but why would it continue to show a call for heat???? I'm stumped.
I don't know why it wouldn't work. As far as I can tell, the only reason for the relay is to isolate the two transformers. That is the one supplying power to the W8665 & the one on the aquastat. Since the X1 & X2 terminals on the 503 are dry contacts, they become the isolation. The only thing I can think of is maybe the transformer on the 503 may not be heavy enough but why would it continue to show a call for heat???? I'm stumped.
#28
Member
Thread Starter
Join Date: Nov 2007
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Well...I don't know what changed but now I do not get 24 vac from either of marked 24vac tabs on the 503. I do get 24vac between the white and red on the zone 2 terminals from the 503.
So I thought I would try and hook up the 8222. White from 503 to #3 relay, Red from 503 to #1 relay, then W from the 8665 to on side of the 8222 coil and R from W8665 to the other side of the 8222 coil.
But I have not ever got the power led to light on the W8665.
I am ready to call a contractor and see if they can figure it out.
Thanks for all your help
Dave
So I thought I would try and hook up the 8222. White from 503 to #3 relay, Red from 503 to #1 relay, then W from the 8665 to on side of the 8222 coil and R from W8665 to the other side of the 8222 coil.
But I have not ever got the power led to light on the W8665.
I am ready to call a contractor and see if they can figure it out.
Thanks for all your help
Dave
#29
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Transformer
If you happen to have another transformer, known to be good, you could wire it directly to the 8665 just to see if you get a power light. Maybe the 8665 is bad???
In any case, once you find out what's going on, please post back & let us know. Hopefully we can all learn something.
In any case, once you find out what's going on, please post back & let us know. Hopefully we can all learn something.
#33
Under what conditions is the auxiliary 24VAC _NOT_ on ?
Perhaps during a priority call for an indirect water heater ?
I could understand that IF you were getting the 24VAC from the R terminal on the zone, as we suggested, but would it matter then if the 8665 were powered down during a priority call ? Not sure it would ... settings memory is all in the transmitter end I think.
Perhaps during a priority call for an indirect water heater ?
I could understand that IF you were getting the 24VAC from the R terminal on the zone, as we suggested, but would it matter then if the 8665 were powered down during a priority call ? Not sure it would ... settings memory is all in the transmitter end I think.
#35
I can't understand why Taco doesn't publish the schematic... I've got half a mind (quiet wise guys!) to purchase one and reverse engineer it and publish the schematic myself ...
Anyone have a schematic of the SR5xx series of panels ?
Anyone have a schematic of the SR5xx series of panels ?