My one zone is warmer than themostat by 10 degrees

One of my zones is warmer than themosta and the baseboards are always luke warm.

I have three zones and three circulators.
 
  #2  
Old 12-12-07, 08:20 AM
O
Banned. Rule And/Or Policy Violation
Join Date: Nov 2007
Posts: 495
Upvotes: 0
Received 0 Upvotes on 0 Posts
The zone control valve is probably leaking through. You need to clean the seat or replace it.
 
  #3  
Old 12-12-07, 10:08 AM
X
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sounds like "ghost flow" from a stuck-open flow-check. You should have a flow-check downstream of each circulator. They usually have an adjustment knob. Try working the knob for the offending (warm) zone, leaving it in the closed (usually clockwise turned to stop) position.

If that doesn't work, or is confusing, take some pics and post them at photobucket and we can walk you through that or other procedure if it's not a stuck flow-check.
 
 