Installing a Taco 571-2 zone valve

Hello,
I currently have 3 zones being serviced by 3 Taco 571-2 zone valves on a Burnham oil furnace. I plan to install an indirect water heater to the system. When I add another zone valve, will I have to install another transformer or will the existing one handle all 4 valves?
 
Sponsored Links
  #2  
Old 12-20-07, 06:49 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,928
Received 0 Votes on 0 Posts
Zone Valve

You don't want to use a zone valve for an indirect. You should use a dedicated circulator. Zone valves restrict the flow too much.
 
  #3  
Old 12-21-07, 08:31 AM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: Pennsylvania
Posts: 2,449
Received 1 Vote on 1 Post
I agree with Grady with the exception if you get a full port zone valve it would be OK. These are hard to find in most supply Houses. If you could get one you would have to add a second transformer or replace the existing transformer with aarger VA transformer. The best way is with a circulator and proper sized piping.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: