Honeywell Aquastat Relay Type L81483

Im in the process of wiring Honeywell (hot water-gas) 3 Zones Honeywell 8043E to Honeywell Aquastat Relay Type L 8148E. There are 3 external wires, red, blue and white. Most of the wiring of zone valves and thermostat is complete. Red wire connects to TV jumpered to W. T is blue wire connection and Z is white wire 24 volts. Blue and white wire connected will start the furnace. Not sure where red or blue wire should go. Can you help. Thanks
 

Last edited by JPhelp; 01-20-08 at 04:52 PM.
Sponsored Links
  #2  
Old 01-20-08, 04:44 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Check the number on the aquastat again please... I don't think the 3 on the end is correct...

Are you replacing the aquastat with the same model ? Should've tagged the wires ...
or taken pics ...
 
  #3  
Old 01-20-08, 04:52 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,078
Received 13 Votes on 11 Posts
L8148

Since it's a gas fired boiler, I suspect the aquastat is an
L8148E. Did a wiring diagram not come with the control?
 
  #4  
Old 01-20-08, 04:54 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I don't think TV should be jumpered to Z ...

Where are these three 'external wires' coming from ?

What boiler are you running ?
 
  #5  
Old 01-20-08, 05:17 PM
Member
Thread Starter
Join Date: Jan 2008
Location: New York
Posts: 2
Received 0 Votes on 0 Posts
L8148E Aquastat

Originally Posted by Grady View Post
Since it's a gas fired boiler, I suspect the aquastat is an
L8148E. Did a wiring diagram not come with the control?
Internally the screw marked TV and the screw marked W is jumpered together and is the external red wire. T is the external blue wire and Z is the white wire that comes out is 24 volts. Im not sure where to hook up the red and blue wire neither one is a hot wire. The name of the furnace is Crown-Aruba which is a gas hot water heater. No, a wiring diagram did not come with the control. I have called Honeywell, no help. JPhelp
 
  #6  
Old 01-20-08, 05:21 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,078
Received 13 Votes on 11 Posts
Crown Aruba

Here's a link to the manual. http://www.crownboiler.com/manuals/c...20ABF-EID).pdf
 
  #7  
Old 01-20-08, 05:22 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Did you buy a used control on e-bay or something ?

They don't come from Honeywell with 'external wires', nor are they jumpered that way ...

Would you please check the model on the aquastat again and tell us if it is indeed an L 8148 E ? There is no such thing as an L81483 ... at least Honeywell doesn't recognize that number, and neither do I ...

Grady, you know them Crowns pretty well...(oops, crossed in the ether!)
 
  #8  
Old 01-20-08, 05:29 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I'm gonna go out on a limb here...

Take the three "external wires" off and throw them away.

Move the jumper from where it is to between Z and W .

Wire the RED wires from the endswitches of the zone valves to T and TV .

You used an external 40VA transformer to power the zone valves, correct ?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: