Aquastat accuracy
Is there anyway to check the accuracy of your aquastat and boiler temp. / pressure gage…neither seems to be accurate.
Mark S.
Mark S.
#2
One has got to fairly accurate. Maybe they both are. If the gauge and control are not in the same place they will read differently. If the height is different or in different sections or one in a pipe they will not and cannot read the same. I have seen differences of 15-20 degrees and both were accurate.
#3
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes
on
39 Posts
Temperature/Pressure Gauge
Rbeck pretty well covered the temperature part. To check pressure, you can get a gauge from most home centers which will screw onto a hose bib on the boiler. Just install the gauge & open the hose bib.
#4
The thing I don't like about them is that the gauge is either gonna be 0-200 PSI or 0-300 PSI ... I can't imagine what Watts is thinking ?! Does ANYONE have a water system that will produce that much pressure ? (these are intended for use with sprinkler systems, but work for boilers too). The gauge resolution is pretty p!$$ poor for pressures under 40 PSI.
The brass fitting is pretty nice, and takes a standard NPT thread for the gauge. So, for a few bucks more, pick up a 0-50 or 0-30 PSI gauge at the plumbing supply and replace the one that comes with the unit.
The brass fitting is pretty nice, and takes a standard NPT thread for the gauge. So, for a few bucks more, pick up a 0-50 or 0-30 PSI gauge at the plumbing supply and replace the one that comes with the unit.
#5
Member
Thread Starter
Join Date: Jan 2008
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have a Weil Mclane WTGO -4 although I no longer make DHW with the coil. I have an indirect fired DHW tank. I was just asking because the high limit is set at 180 degrees but when the burner shuts down on high limit the temp gage reads around 210 degrees… thanks for your thoughts.
Mark
Mark
#6
Mark, if you are seeing that temp minutes after the burner shuts down, and the heat call is finished, the circ has stopped, it's probably from 'heat soak' ... the heat trapped in the boiler iron is transferring to the water.
#7
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
I haven't looked for a while but I think that you can pick up pressure gauges that are 0-60 psi in the pumps section of the big box stores. All you need then is a 3/4 to 1/4 bushing and the 3/4 inch pipe to hose thread adapter. Any plumbing supply store should have a number of gauges in whatever range you desire.
As for "accuracy" in thermometers, pressure gauges and aquastats...most are manufactured to a fairly "loose" tolerance of one-to-two percent of the full-scale reading. Rough handling can easily jar them from absolute accuracy. Far more important than absolute accuracy is repeatability, that is the ability to indicate (or in the case of the aquastat, actuate) at the same point whenever the same temperature or pressure is sensed regardless of whether or not the indicated pressure or temperature is exactly correct.
As for "accuracy" in thermometers, pressure gauges and aquastats...most are manufactured to a fairly "loose" tolerance of one-to-two percent of the full-scale reading. Rough handling can easily jar them from absolute accuracy. Far more important than absolute accuracy is repeatability, that is the ability to indicate (or in the case of the aquastat, actuate) at the same point whenever the same temperature or pressure is sensed regardless of whether or not the indicated pressure or temperature is exactly correct.