Vent Damper Wont Stop cycling until I hit it.

Ive got a 20 year oldWeil-McLain hot water boiler that works great.
But over the past two years it wont fire up (about once a week), until I go down and bang on the duct with the vent damper in it.
The Vent damper is continuosly turning until I bang on it. Then it stops and the furnace fires up.
I would say the frequency has doubled from once a week to 3 times a week. The Vent damper is a johnson Mizer #M15AC.
Any suggestions?
 
  #2  
Old 02-27-08, 02:47 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Originally Posted by crownm View Post
Any suggestions?
Replace it. It don't owe you a dime, and it's a safety issue.
 
  #3  
Old 02-27-08, 02:50 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Vent Damper

Most vent dampers have a switch in them which closes when the damper comes to it's open position, stops the damper motor, & allows the burner to fire. Sounds like the switch has gone bad. I'm not at all familiar with that particular damper thus I can't tell you if the switch is replaceable or not.
 
 