Repairing Residential Boiler Piping??
#1
Member
Thread Starter
Join Date: Oct 2006
Posts: 52
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Repairing Residential Boiler Piping??
Hello everyone,
I have a fifty year old residential hot water baseboard heating system with 3/4" copper piping. I would like to repair some leaks at piping fittings and manual shut off valves. Some of the locations are very tight to wooden structure and difficult to work on - - especially when soldering copper.
It is my understanding that there are newer and more
flexible (plastic / synthetics) piping materials being used today for residential boiler piping that don't require soldering. I am not sure that I will be able to make these repairs myself, but would like to be somewhat knowledgeable about what's possible and what's not - - and potential material compatibility problems.
Would appreciate your comments and suggestions on work that I would like to have completed before the heating season.
Thanks,
Bob
I have a fifty year old residential hot water baseboard heating system with 3/4" copper piping. I would like to repair some leaks at piping fittings and manual shut off valves. Some of the locations are very tight to wooden structure and difficult to work on - - especially when soldering copper.
It is my understanding that there are newer and more
flexible (plastic / synthetics) piping materials being used today for residential boiler piping that don't require soldering. I am not sure that I will be able to make these repairs myself, but would like to be somewhat knowledgeable about what's possible and what's not - - and potential material compatibility problems.
Would appreciate your comments and suggestions on work that I would like to have completed before the heating season.
Thanks,
Bob
#2
Temporarily Suspended
Join Date: Jul 2008
Location: NY
Posts: 10,265
Upvotes: 0
Received 0 Upvotes
on
0 Posts
There is a great new coupling for copper pipes that elminate solder. They are called Shark Bite and they are sold at home depot. I don't understand why they aren't popular. You just twist and push to connect 2 pipes. They even have Tees and elbows. It's easier than Leggos.
#3
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Shark Bite
I've used them many times on domestic water but I don't know if they would take the higher temps of a heating system.
There are ceramic fiber "blankets" with a heavy foil or light sheet metal backing which are often used as heat shields when soldering near combustables. There are also chemical compounds such as LA-CO Cool Gel heat barrier spray. http://www.laco.com/
There are ceramic fiber "blankets" with a heavy foil or light sheet metal backing which are often used as heat shields when soldering near combustables. There are also chemical compounds such as LA-CO Cool Gel heat barrier spray. http://www.laco.com/
#5
I was curious so I checked out Cash-Acme for the specs...
So, it appears that if you are careful not to exceed 200°F, you would be OK in a hydronic system.
The SharkBite® push-fit fittings have been design certified and listed to ASSE 1061/NSF 61. The SharkBite® push-fit fittings are listed by IAPMO and are certified for potable and hydronic heating water distribution (note: Glycol mixture for hydronics is not to exceed 50% concentration). The SharkBite® push-fit fittings have been certified for underground applications and as a manufactured joint without access panels and they meet UPC, IPC and cUPC requirements.
Instant push-fit connection for increased ease of use. Certified to 200 psi and 200°F (93°C). Fits OD controlled copper, CPVC, or PEX pipe. Body composed of solid DZR brass.
Instant push-fit connection for increased ease of use. Certified to 200 psi and 200°F (93°C). Fits OD controlled copper, CPVC, or PEX pipe. Body composed of solid DZR brass.
#7
Member
Thread Starter
Join Date: Oct 2006
Posts: 52
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Repairing Residential Boiler Piping
Hey guys,
You have given me a whole lot to check out.
Grady - I am on my way to look at the "Laco" web site that you have recommended - - for the "Cool Gel" heat barrier spray.
Pulpo & NJ Trooper - I am also going to search for "Sharkbite" on the internet. Based on what you have indicated I might be able to use these fittings on my hot water heating system copper piping - - that would be a nice solution.
Do appreciate the comments,
Thanks again,
Bob
You have given me a whole lot to check out.
Grady - I am on my way to look at the "Laco" web site that you have recommended - - for the "Cool Gel" heat barrier spray.
Pulpo & NJ Trooper - I am also going to search for "Sharkbite" on the internet. Based on what you have indicated I might be able to use these fittings on my hot water heating system copper piping - - that would be a nice solution.
Do appreciate the comments,
Thanks again,
Bob
#8
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Shark Bites
Just a heads up on the Shark Bite fittings: Make sure you get real Shark Bite fittings. They are made by Cash-Acme & are quite heavy for their size due to the brass. I would not use the plastic imitations.