Expansion tank size?

Anyone know what determines the size of the expansion tank you need in your boiler system? Does it depend on total amount of water in system, highest height of radiation piping, size of pumps, size of boiler, or other? Should an old tank (I have a huge one on my ancient system at basement ceiling level) be routinely replaced when a new system is put in - if so by what size?
 
  #2  
Old 10-06-08, 06:30 PM
X
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes on 0 Posts
www.amtrol.com

they have a sizing guide.

The simplest way is to fill the system with water (minus the old expansion tank), then drain it into a 5 gallon bucket until it's empty. A converted gravity system might have 100 gallons in it.

I would definitely go with a bladder tank(s) and ditch the old one.
 
  #3  
Old 10-06-08, 07:27 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Water volume, and the min-max water temperatures determine the size of the tank.

If you have 100 gallons, and heat the water from 70 to 180, you will have roughly 104 gallons. Your tank needs to be big enough to admit that 4 gallons of expanded water.

Keep in mind that if you do ditch the old tank, you will also need to add an air separator and an automatic air vent in addition to the new tank. You can't simply connect the new tank to the old pipe... well, you _could_ but then the air that's in the system would have no way out, where it used to (hopefully) find it's way back into the expansion tank. But you don't want it there with a bladder tank.
 
  #4  
Old 10-07-08, 06:28 AM
J
Member
Thread Starter
Join Date: Sep 2008
Location: USA
Posts: 34
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for this excellent explanation and link. Given my 4" c.i. main heating run and radiator sizes, it sounds like I may need more than one tank - more measurements needed!
 
  #5  
Old 10-07-08, 06:42 AM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,394
Upvotes: 0
Received 61 Upvotes on 51 Posts
You can find the water volume in radiation and piping here. Look under the water column at the last two choices. You will have to add the boiler water volume which you should get from the manufacturer.
If you have copper tube baseboard use the manufacturers chart. They do vary the size from one to another.
http://www.comfort-calc.net/tech_area_index.htm
 
 