Hot Water Heat Temperature Control

I have an old ARCO/Ideal heater driving a convection fed hot water/radiator system. The water temperature is manually set, but it needs to go higher when it's colder outside, and lower when I need heat but it's not so cold. Is there an automated way to do that? Generally (night time temps at 20(+/-5)F), the heater will get the system up to heat (120F) in 20-30 minutes or so, and the cast iron will dissipate it over a few hours, so the whole system runs less than an hour a day 95% of the time, but it needs to get to a higher temp (150F) when the outside temp approaches 0. Best case is it automates to a inverted scale evenly over that range.
 
Sponsored Links
  #2  
Old 10-27-08, 05:31 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
When you write "convection fed" do you mean a gravity system with no circulating pump?

An outdoor reset system would automatically change the temperature setting on the boiler inverse to the outdoor temperature. One of the old dual-bulb aquastat models would be ideal for you, if you could find one.
 
  #3  
Old 10-28-08, 08:41 AM
Member
Thread Starter
Join Date: Oct 2008
Location: Oklahoma City
Posts: 3
Received 0 Votes on 0 Posts
Originally Posted by furd View Post
When you write "convection fed" do you mean a gravity system with no circulating pump?

An outdoor reset system would automatically change the temperature setting on the boiler inverse to the outdoor temperature. One of the old dual-bulb aquastat models would be ideal for you, if you could find one.
Yes, there is no circulation pump. Works great, no noise, no electric requirement. I'll research the dual bulb aquastat. Thanks.
 
  #4  
Old 10-28-08, 09:50 AM
Member
Thread Starter
Join Date: Oct 2008
Location: Oklahoma City
Posts: 3
Received 0 Votes on 0 Posts
The current high water temp limit switch is a Honeywell Ambi-stat Type-L4008C Model-T4013E, which appears to be a single bulb simple high temp limit/cutoff switch which opens when the set temperature is reached. So the current control is the the themostat calls for heat, closing the circuit, initiating the furnace firing, when the water gets to the high temp limit, the circuit is opened, closing the gas valve which feeds the burner. So long as the thermostat is calling for heat, the high limit switch will cycle the burner valve open/close to keep the water hot enough. I'm not sure what the water temp cycle range is, or how to find out.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: