Just installed WM Ultra 3 105 boiler about three weeks ago. Things have been working fine for two weeks. However, in the last week the boiler locked up three times. The error message is "Supply too fast." Is this some thing that is easily solved? I tried to call WM. However, they will not entertain calls from home owners.
GEEVEE
GEEVEE
#2
I'm modcon stupid ... Supply Too Fast ? ... the manual don't tellya what that means ?
Maybe it's measuring the Delta T across the heat exchanger, and it's not enough ? making it think there is too much flow through the boiler ?
Did you happen to notice my last comments on your photos ?
The question about the purge tee being in a partial position ? In normal operation, that valve should be wide OPEN.
And that ball drain on the left of the heating loop ? the one that is OPEN in the picture which should be CLOSED during normal operation ?
Maybe it's measuring the Delta T across the heat exchanger, and it's not enough ? making it think there is too much flow through the boiler ?
Did you happen to notice my last comments on your photos ?
The question about the purge tee being in a partial position ? In normal operation, that valve should be wide OPEN.
And that ball drain on the left of the heating loop ? the one that is OPEN in the picture which should be CLOSED during normal operation ?
#3
Supply too fast
I think it does mean the flow rate in the boiler is too high. Could be related to valve settings. Can't maintain it's Delta T target ... mostly guesses... and googles ...
#4
Who ...
On second thought, and more reading, maybe it means that the SUPPLY temperature rose TOO FAST ... I think that's CODE 25 ?
Which might indicate that a pump is NOT pumping ...
I think WHO might have these codes memorized... he'll be along soon .
Which might indicate that a pump is NOT pumping ...
I think WHO might have these codes memorized... he'll be along soon .
#5
NJ, it does mean the water temperature rose to quickly. It has to do with flow. What is restricting flow? How is it piped. NJ you mentioned Geevee had pic's. Do you know if they are still around?
#6
Member
Thread Starter
Join Date: Sep 2008
Location: NEW YORK METRO
Posts: 23
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Rbeck: Here is the thread on my installation.
http://forum.doityourself.com/boiler...ld-boiler.html
NJ Trooper: The purge tee valve is wide open. The ball drain on left side in now kept closed. The boiler circulator is running. The following are the temparature readings when the lockout condition occured the last three times.
System supply 115 150 144
System Return 152 164 154
Boiler Out1..... 158 172 160
Boiler Out2..... 156 170 159
Boiler In......... 142 153 151
Flue1............. 159 173 141
Flue2............. 159 171 140
Outdoor......... 40 40 42
I hope this helps
GEEVEE
http://forum.doityourself.com/boiler...ld-boiler.html
NJ Trooper: The purge tee valve is wide open. The ball drain on left side in now kept closed. The boiler circulator is running. The following are the temparature readings when the lockout condition occured the last three times.
System supply 115 150 144
System Return 152 164 154
Boiler Out1..... 158 172 160
Boiler Out2..... 156 170 159
Boiler In......... 142 153 151
Flue1............. 159 173 141
Flue2............. 159 171 140
Outdoor......... 40 40 42
I hope this helps
GEEVEE
#10
Member
Join Date: Nov 2008
Location: New York
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Did you ever figure out why it was locking out. I have the same problem with mine. It goes to lockout with an error message about supply too fast. I noticed that it happened when heating zone is on and then the domestic goes on to priority. The unit resets itself after a minute and everything works fine then. Anyone have any ideas??
#12
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes
on
0 Posts
rbeck, the album with his pictures, pictures, pictures starts here:
Image of The Complete Picture - Photobucket - Video and Image Hosting
Image of The Complete Picture - Photobucket - Video and Image Hosting
#14
Member
Join Date: Nov 2008
Location: New York
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok this is a picture of the install allmost complete (note that one zone has no piping going to it and the blue flex pipe is just for a temp feed to the outdoor shower.
All piping is 1" for the primary and reduces down to 3/4" for the zones. The only thing that I can think of that is a little unconventional is that I piped the heating zones off the top of the boiler and the DHW off the bottom. I called Weil Mclain about this prior to doing the installation and they said it wouldn't be a problem.
I have about 20 feet of 1" pipe between the boiler and the domestic hot water tank with 10 1" 90's, 2 ball valves and a taco 0011ifc pump. I checked the pump curve for the 0011ifc and I should be getting enough flow.
I also checked the error codes for the boiler and it seems that it's going out on the call for DHW.
Any ideas?
http://i494.photobucket.com/albums/r...e/IMG_1381.jpg
All piping is 1" for the primary and reduces down to 3/4" for the zones. The only thing that I can think of that is a little unconventional is that I piped the heating zones off the top of the boiler and the DHW off the bottom. I called Weil Mclain about this prior to doing the installation and they said it wouldn't be a problem.
I have about 20 feet of 1" pipe between the boiler and the domestic hot water tank with 10 1" 90's, 2 ball valves and a taco 0011ifc pump. I checked the pump curve for the 0011ifc and I should be getting enough flow.
I also checked the error codes for the boiler and it seems that it's going out on the call for DHW.
Any ideas?
http://i494.photobucket.com/albums/r...e/IMG_1381.jpg
#15
Maybe...
just a wild guess...
When a zone is calling, hot water flowing ... and the DHW calls ... that 20' of 1" pipe has a good size 'slug' of cool water in it ... maybe the slug is being detected by the sensors ... and generating the error message.
When a zone is calling, hot water flowing ... and the DHW calls ... that 20' of 1" pipe has a good size 'slug' of cool water in it ... maybe the slug is being detected by the sensors ... and generating the error message.
#16
Member
Join Date: Nov 2008
Location: New York
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok I reset all the diagnostic error counts and I'll wait and see if I can track it down to exactly when it happens. It doesn't lockout on every call for DHW so it's kind of difficult to find out what the problem is.
All the digital supply and return temps on the boiler seem to correspond to what is on the analog gauges.
I also don't think that 20 feet of pipe is too excessive, 10 feet there and 10 back.
My gut feeling is that on the initial call for DHW, it's drawing in some hot water from the heating zone and raising the "supply temp too fast" Thats why it it only seems to be happening when the DHW gets a call after the heat is on.
All the digital supply and return temps on the boiler seem to correspond to what is on the analog gauges.
I also don't think that 20 feet of pipe is too excessive, 10 feet there and 10 back.
My gut feeling is that on the initial call for DHW, it's drawing in some hot water from the heating zone and raising the "supply temp too fast" Thats why it it only seems to be happening when the DHW gets a call after the heat is on.
#17
I wouldn't put a whole lotta stock on those 'error messages' being very specific ... lookit GEEVEE's case ... he got the same message, and the sensors were reversed ! The return was hotter than the supply ... they may generate the same error message for a number of conditions ...
Maybe that message is generated any time any one of the sensors changes too quickly ... cold to hot ... hot to cold ... return hotter than the supply !
But, there are two lockouts on your guyz'z boilers, 'soft' and 'hard' lockouts ... It seems that yours is a soft lockout because it's resetting itself, but GV's was a hard lockout I believe ?
So it seems that the same error message can apply to a number of conditions / problems ...
Maybe that message is generated any time any one of the sensors changes too quickly ... cold to hot ... hot to cold ... return hotter than the supply !

But, there are two lockouts on your guyz'z boilers, 'soft' and 'hard' lockouts ... It seems that yours is a soft lockout because it's resetting itself, but GV's was a hard lockout I believe ?
So it seems that the same error message can apply to a number of conditions / problems ...
#18
Member
Join Date: Jul 2009
Location: Pennsylvania
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
July 24, 2009 - Suppy too Fast WM S3 155
July 24, 2009 - WM Series 3 155
Boiler installed May 2009.
Have same problem. Happens about 1/week. Contractor and
WM rep here. WM rep suggest install changes, addt'l piping,
third and larger pump for indirect h20 heater, move sensors
further up pipe.. Also suppled new control board for boiler.
NO LUCK. All that was done and still had the problem.
Directed my contractor to this forum for research.
Contractor and WM rep due here nex Friday.
Interesting that the original posting for this forum string is
Sept 2008 and still the WM guy had nothing definitive
to fix it.
According to my manual, when the supply water temp rises faster than 2 degress F/second, a counter is incremented.
When that counter reaches 5, the boilier is locked out.
Resetting the message, resets the counter and unlocks
the boiler.
.....and the beat goes on
Boiler installed May 2009.
Have same problem. Happens about 1/week. Contractor and
WM rep here. WM rep suggest install changes, addt'l piping,
third and larger pump for indirect h20 heater, move sensors
further up pipe.. Also suppled new control board for boiler.
NO LUCK. All that was done and still had the problem.
Directed my contractor to this forum for research.
Contractor and WM rep due here nex Friday.
Interesting that the original posting for this forum string is
Sept 2008 and still the WM guy had nothing definitive
to fix it.
According to my manual, when the supply water temp rises faster than 2 degress F/second, a counter is incremented.
When that counter reaches 5, the boilier is locked out.
Resetting the message, resets the counter and unlocks
the boiler.
.....and the beat goes on

#20
Member
Join Date: Dec 2008
Location: Conway NH
Posts: 38
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I wish I got paid for every time a "Rep" sat in front of his product and scratched his head.
Most of the time it ends up being a stab in the dark guess.(Or what he thinks may be the unprovable manufacturing defect) He then sends a new boiler and away we go.

Most of the time it ends up being a stab in the dark guess.(Or what he thinks may be the unprovable manufacturing defect) He then sends a new boiler and away we go.