heat loss calculation and chosing a boiler

Reply

  #1  
Old 11-16-08, 10:34 AM
Z
Member
Thread Starter
Join Date: Oct 2008
Location: NYC
Posts: 433
Received 0 Votes on 0 Posts
heat loss calculation and chosing a boiler

After calculating the heat loss, what is that number matched up with that up with on the boiler ratings?

Is it the DOE Heating Capacity, net IBR net rating or input mbh?
 
Sponsored Links
  #2  
Old 11-16-08, 01:19 PM
X
Member
Join Date: Nov 2005
Location: USA
Posts: 2,459
Received 0 Votes on 0 Posts
The answer depends somewhat on the fuel type, heating system type, potential overestimate of the heat loss (typically 10-30%) and other factors, but in general, the DOE heating capacity will do.
 
  #3  
Old 11-16-08, 03:52 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Posts: 2,482
Received 5 Votes on 4 Posts
Agreed DOE output. Been using that for about 15 years and have never had a problem.
xiphias I didn't see you around here for awhile or maybe I just missed your posts.
 
  #4  
Old 11-16-08, 05:28 PM
Who's Avatar
Who
Who is offline
Member
Join Date: Jan 2006
Location: San Jose
Posts: 2,175
Received 0 Votes on 0 Posts
It seems that often enough the true heatload is only 2/3rds of the calculated heatloss. Personally, of the gross output would be well within my comfort level as a guess. AJHs might disagree. Around here for those of us who actually do pull a permit, IBR must equal or exceed the calculated heat loss which is nuts.

My calculated heatloss was 56 MBH. At design day temps my boiler doesn't hit 40 MBH and that's gross input at the meter.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: