Honeywell pressuretrol settings

My upper radiators on my steam system do not heat up as well as the lower floor, in fact at night the bedroom is chilly. My settings on the pressuretroll are 1/2 psi and diff of 2lbs. If i was to increase the diff slightly, would i get the steam to the upper floors, i know i would probably use more oil if i do this, just wanted some input on this. The vent valves have been replaced, and are working properly also, the boiler is only about 8 years old. Thanks Jim
 
  #2  
Old 11-23-08, 05:02 AM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,394
Upvotes: 0
Received 61 Upvotes on 51 Posts
It is not a pressure problem. You can heat a 10 story building a city block square with 2 psi. Do you have main line vents? What type thermostat do you have? Is the boiler properly sized? Is it piped properly?
How about some pictures.
 
  #3  
Old 11-23-08, 05:08 AM
J
Member
Thread Starter
Join Date: Apr 2002
Location: new jersey
Posts: 60
Upvotes: 0
Received 0 Upvotes on 0 Posts
reply to post

Yes i have what looks like 2 vent valves in the main piping above the boiler, i do believe they are both working, the system is a Weil McClain oil fired boiler with the hartford loop, unit works fine, just that the rooma upstairs dont heat up like the lower rooms. Thanks for the reply. I appreciate it. Jim
 
  #4  
Old 11-23-08, 05:12 AM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,394
Upvotes: 0
Received 61 Upvotes on 51 Posts
It takes ounces of pressure to heat a home. If not it comes to piping, venting and even insulation.
Is all the piping in the basement insulated? If not it will condense the steam too fast and slow the heating process. It could be as much as a thermostat adjustment.
Proper piping includes more than a hartford loop.
 
  #5  
Old 11-23-08, 09:11 AM
J
Member
Thread Starter
Join Date: Apr 2002
Location: new jersey
Posts: 60
Upvotes: 0
Received 0 Upvotes on 0 Posts
reply to post

Ok the pipes are insulated in the basement, i even took the vent valve off the side of the radiator and ran the boiler, the radiator heats up to the 1st section on the radiator and then no more, can the radiator be clogged with rust or something, i hear air trying to come through the hole where the valve is, but no steam is coming through, what gives here. Thanks Jim
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: