thermostat to white rogers zone valve

I have to wire a honey well themostate to a white rogers zone value. The W/R zone value has numbers 2, 5, 4. 6, 1, 3 while the thermostat has wires red, white green. I have the W/R wiring diagram which uses numbers not colors. I need to know what colors correspond to what number.
Thank you for any help. E J Bear
 
Sponsored Links
  #2  
Old 11-26-08, 04:58 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Do you have the model number for the zone valves and the thermostat handy ? We would be guessing without knowing that much ...
 
  #3  
Old 11-27-08, 08:35 AM
E
Member
Thread Starter
Join Date: Nov 2008
Location: michigan
Posts: 3
Received 0 Votes on 0 Posts
thermostat to white rogers zone valve

The thermostat is a Honeywell CT87A and the White Rogers zone valve is 1311-102.
ejbear
 
  #4  
Old 11-27-08, 11:25 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I don't believe that thermostat will work with the W-R valve.

That valve requires that the thermostat be a true 3 wire thermostat... it has to both power open the valve, AND power it closed. 'Most' zone valves are power open only, and close by themselves when power is removed. The 1311 will stay open. I don't know if they are compatible, but it is possible that the 1361 W-R powerhead will fit that valve body ... the 1361 will work with your thermostat. If your thermostat has three wires, it's because it's a combo heat/cool unit ... those thermostats are just 2 wire for the heating circuit ...

It IS possible to wire up an external relay that would allow you to use the two wire thermostat with that valve ... are you up for hooking up a relay ?
 
  #5  
Old 11-27-08, 12:36 PM
E
Member
Thread Starter
Join Date: Nov 2008
Location: michigan
Posts: 3
Received 0 Votes on 0 Posts
thermostat to white rogers zone valve

Yes, I'm up to rigging a relay.
ejbear
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: