Boiler Operating Pressures

Reply

  #1  
Old 12-02-08, 11:12 AM
S
Member
Thread Starter
Join Date: Dec 2008
Location: Western Canada
Posts: 40
Received 0 Votes on 0 Posts
Boiler Operating Pressures

I have a cast iron boiler with 4 zone valves. The limit switch is set at 160F(Low)-180F(High). The gauge reads around 11-12 psi(Low) and cuts off at 19 psi(High). Had a new expansion tank installed but was wondering if there should be consistant pressure on the gauge or is it quite normal that when the boiler is firing the pressure is going up and dropping when it it hits the LL limit switch? The PSV is set for 25 PSI but also curious if 11-12Psi could be a warning for low water level? Any advice as I am trying to figure this out. This is on a 4-plex.
Thanks
 
Sponsored Links
  #2  
Old 12-02-08, 01:37 PM
G
Member
Join Date: Oct 2008
Location: USA
Posts: 2,954
Received 10 Votes on 10 Posts
The system pressure will normally increase several psi as the boiler heats up. 12-15 psi when the boiler is cold is typical for a 2-story house with the boiler in the basement.

The cold pressure is established by the setting on the automatic feedwater pressure regulator that should be connected to the city water supply. The hot pressure increase depends on the size of the expansion tank in relation to the total volume of the system.

Low water level is not indicated by your numbers. Low level is pretty difficult to come by with a hot-water system that is properly filled, etc.
Doug
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: