Air in baseboard hot water system?


  #41  
Old 12-26-08, 05:53 PM
Dennis Lee's Avatar
Member
Join Date: Dec 2008
Location: Upstate New York
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Two Scoops

I see online Taco 1-1/4 air scoops for around $20. If I put a couple of those in would they go on the supply side 18 inches on either side of the upright?

The would the bladder tank hang from one of them, or would it be better on the make-up water line?

This looks like a good warm weather project, I think.
 
  #42  
Old 12-26-08, 05:59 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Warm Weather Project

They would, as you said, go at least 18" on each side of the supply riser & the tank could go on the bottom of either. The other would just be plugged.
 
  #43  
Old 12-29-08, 06:53 PM
J
Member
Join Date: Oct 2008
Location: New England (RI)
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Time to weight in and take my licks,
First getting air out of a hot water baseboard system is a PITA. I opened my system to take out a section of baseboard to put a closet door in my second floor bedroom. I got everything soldered back together (so I thought) and started to refill the system. No air bleeds on the second floor and yes, I know I should have put them in.
After trying to bleed using pump/water pressure I've finally realized I have vapor lock it it wont bleed.

First a brief description of my system. 1 pump, 2 zone control valves. pretty solid design.
Heres what I did, I forced the second floor zone on with the first floor off. when the pump was up to pressure I closed the suction side main valve, shut off the pump, opened the drain valve upstream of the shutoff vavle and pulled a vacuum on the line till I had good water flow. Worked great, right up to the point of finding the leaks, 2 out of 14 joints, Now I'm back to draining and re sweating. Sucks to be me.

Any Hints?
 
  #44  
Old 12-29-08, 09:23 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Any Hints?
Pressure test with air before refilling with water.

Don't feel bad about being you, you have no idea how much it 5uck5 to be me!

"Thy burden is greater than mine"
 
  #45  
Old 12-30-08, 01:39 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
As long as you have to drain the system to re-solder those joints why don't you go ahead and install the vent valves? Vents should be at any high point and at the outlet of any baseboard that turns downward.
 
  #46  
Old 12-30-08, 02:59 AM
J
Member
Join Date: Oct 2008
Location: New England (RI)
Posts: 8
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pressure test, yes! should have done it. lacked a fitting to connect my compressor.

air valves, If I can fit them.

Thanks guys
 
  #47  
Old 12-30-08, 11:49 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Air Valves

Don't use automatic air vents on baseboard. Use only the manual type. Certainly should fit under any baseboard cover with no problem.
 
  #48  
Old 01-02-09, 05:08 AM
E
Member
Join Date: Jan 2009
Location: New England
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Jumping in here rather than starting another thread on the same topic. I'm new here and relatively new to this type of work but I've been able to glean some knowledge here and there while searching the internet.

Here's my system, about as basic as it gets:


I don't have bleeders at the baseboards so I've been trying to purge air at the boiler which is why the hose is there but it doesn't seem to be working. I close valve 1, open spigot 2 and after an initial trickle of water nothing comes out. The cap at 3 is loose and the water inlet at 4 is open. If I manually add water with the lever on top of the pressure reducer the boiler pressure goes up but I still get nothing out of the hose. I'm stumped...and cold, please help.
 
  #49  
Old 01-02-09, 07:36 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Weird!...

That green thing to the left of the air scoop and expansion tank is a 'flow check' valve. There's a 'disc' inside that gets pushed up to allow flow when the pump is running, but falls down again when the pump stops to prevent 'ghost flow' in the system.

Perhaps that disc is 'stuck' ... the knob on top should manually lift that disc by turning counter clockwise. Try that. It will probably free up the disc if that's the problem. Remember to return it to clockwise when yer done.

Check ALL the piping for any other valves that may have been inadvertently closed.

Another thing you can try just as a 'sanity check' ... with the boiler COOLED below 100°F, open valve 4 and lift the lever on the regulator valve. You should get flow through the boiler and out the hose. That will prove that the valve is supplying enough water. It may be that the valve is plugged partially and only allowing a trickle of water ... although since you say the pressure builds in the boiler, may not be the problem... but easy enough to check. You should get a decent flow ...

Perhaps the reason you are having an issue with air in the system is due to some other underlying reason ... maybe related to the feedwater regulator also ... what are the operating pressures on the boiler when it's HOT and when it's COLD ?

By the way, this is an excellent time to check/adjust the air charge on the expansion tank. If you can't find the instruction to do so in one of the other recent posts here, let me know ...
I'll retype it if I have to ... but there are several recently.
 
  #50  
Old 01-02-09, 08:08 AM
E
Member
Join Date: Jan 2009
Location: New England
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by NJ Trooper View Post
Weird!...

That green thing to the left of the air scoop and expansion tank is a 'flow check' valve. There's a 'disc' inside that gets pushed up to allow flow when the pump is running, but falls down again when the pump stops to prevent 'ghost flow' in the system.

Perhaps that disc is 'stuck' ... the knob on top should manually lift that disc by turning counter clockwise. Try that. It will probably free up the disc if that's the problem. Remember to return it to clockwise when yer done.
No luck, I opened the check valve, heard a little gurgling but now the check valve is leaking after I reclosed it.

Originally Posted by NJ Trooper View Post
Check ALL the piping for any other valves that may have been inadvertently closed.
Done and none.

Originally Posted by NJ Trooper View Post
Another thing you can try just as a 'sanity check' ... with the boiler COOLED below 100°F, open valve 4 and lift the lever on the regulator valve. You should get flow through the boiler and out the hose. That will prove that the valve is supplying enough water. It may be that the valve is plugged partially and only allowing a trickle of water ... although since you say the pressure builds in the boiler, may not be the problem... but easy enough to check. You should get a decent flow ...
No flow at all.

Originally Posted by NJ Trooper View Post
Perhaps the reason you are having an issue with air in the system is due to some other underlying reason ... maybe related to the feedwater regulator also ... what are the operating pressures on the boiler when it's HOT and when it's COLD ?
Looks to be just under 20psi hot, it's still cooling now.

Originally Posted by NJ Trooper View Post
By the way, this is an excellent time to check/adjust the air charge on the expansion tank. If you can't find the instruction to do so in one of the other recent posts here, let me know ...
I'll retype it if I have to ... but there are several recently.
Got it, on that now.
 
  #51  
Old 01-02-09, 09:11 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
but now the check valve is leaking after I reclosed it.
Just below the knob, there is a gland nut, and below that is the big-a55 nut that holds the whole thing together. Under the gland nut is a 'packing' that seals the stem. I'm guessing that's where it's leaking now? If so, tighten that gland nut just a wee bit, only enough to stop the leak. That will squeeze the packing a bit tighter and seal the stem.

No flow at all.
It sure does sound as though the regulator is plugged up ...

How 'adventurous' do you want to get?
 
  #52  
Old 01-02-09, 09:52 AM
E
Member
Join Date: Jan 2009
Location: New England
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by NJ Trooper View Post
Just below the knob, there is a gland nut, and below that is the big-a55 nut that holds the whole thing together. Under the gland nut is a 'packing' that seals the stem. I'm guessing that's where it's leaking now? If so, tighten that gland nut just a wee bit, only enough to stop the leak. That will squeeze the packing a bit tighter and seal the stem.



It sure does sound as though the regulator is plugged up ...

How 'adventurous' do you want to get?
I should add here that the inlet regulator was replaced about a year ago and does seem to be functioning fine. If I open valve 1 and 4 while the spigot at 2 is open i get a nice steady flow of water. At this point I've thrown in the towel and I've made a service call to the heating company that does my annual boiler service. I suspect at this point that it may be the check valve but I'll be sure to let you know when I do find out what the issue is. Thanks for trying to help!
 
  #53  
Old 01-02-09, 11:56 AM
E
Member
Join Date: Jan 2009
Location: New England
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Well, I feel like a dummy. I hadn't been running the baseboards much since we installed a wood stove this year and well, one of the pipes, right above the garage door was frozen. $100 and a hole in the ceiling later, I know what the problem was and where to find it next time. Beer 4U2
 
  #54  
Old 01-02-09, 05:28 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Naaahhhh, no dummy ... we've all been there!

A lesson learnt...

Good Luck!
 
  #55  
Old 01-02-09, 05:42 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Cheap Lesson

If you got away for $100, you got away cheap. And learned a lesson too? Way Cheap. Beer 4U2
 
  #56  
Old 01-04-09, 10:55 AM
T
Member
Join Date: Jan 2009
Location: Northeast US
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sloshing Sound

Great reading through this thread. I recently replaced the TACO circulator on my system as I was not getting any circulation through my baseboard heating. Seems to be working fine, however when my thermostat calls for heat and the system goes into action, I hear a loud sloshing noise for about 10 seconds. This goes away for the most part, but I occasionally hear the sound of water sloshing through the pipes. All gages check out normal, with levels as you have suggested. Also checked pressure in overflow tank and that reads 14psi.
Is this sloshing sound normal, or is there air in the system? If so, how do I bleed?
Thanks.
 
  #57  
Old 01-04-09, 12:40 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Sloshing Sound

What you are hearing is due to air. Some pictures of the boiler & nearby piping would help. You can post them on photobucket.com or similar site & provide a link here.
 
  #58  
Old 01-06-09, 07:33 AM
T
Member
Join Date: Jan 2009
Location: Northeast US
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pictures

Thanks for the reply. Here are some photos:

tjh22 - Photobucket - Video and Image Hosting

As the photos indicate, this is a two-zone system, but Zone 1 is shut down due to renovation.

Any instructions you can pass along so I can get the air out of my system would be most appreciated.

Thanks again.
 

Last edited by tjh22; 01-06-09 at 08:19 AM. Reason: Revised URL
  #59  
Old 01-06-09, 05:56 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Pix

Thanks for the pictures. Big help.
In picture 3 it appears there are purge valves (red handled hose bibs above the yellow handled ball valves). It would also appear the zone being renovated to be shut down via the ball valve.

To purge, connect a hose to the other red valve, close the yellow, manually lock open the zone valve, put the other end of the hose into a bucket, & open the red valve. Allow water to flow until you no longer get air bubbles.
 
 