Pics of my new boiler install
#1
Member
Thread Starter
Pics of my new boiler install
Old boiler and prep pics posted right now. Progress pics posted as things go the next 2 days.
(why does there have to be an ice storm of all days today?
)








(why does there have to be an ice storm of all days today?










#2
Member
Thread Starter
#3
Member
Join Date: Dec 2007
Location: A Galaxy From Afar
Posts: 337
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Looking at the gray floor standing tank I thought it was a well water supply update. But then seeing the size of the expansion tank on the ceiling, I'm thinking that the gray tank with the blue caps is the new expansion tank?
Looking forward to the final install pic's.
Al.
Looking forward to the final install pic's.
Al.
#4
This would just be me, I wouldn't think of critiquing any sort of boiler install, but....
How the heck do you get to the power panels??? That can't be up to code..is it?
Was this some sort of commercial building? I'm sure there was another thread somewhere, but I don't normally look in the boiler section (unless there are pics to check out...lol)
How the heck do you get to the power panels??? That can't be up to code..is it?
Was this some sort of commercial building? I'm sure there was another thread somewhere, but I don't normally look in the boiler section (unless there are pics to check out...lol)
#5
Gunguy, I wondered about those panels also ... the pictures probably make it look closer than it actually is... but still...
Sorta looks like the kinda mech room you'd expect to see in an old haunted hotel! I expected to see Jack Nicholson peering around a corner...
That is one huge extank, ain't it?
Ohhhh, so it's YOUR fault! 
Just funnin' with ya Lucky... keep the pics coming!
Sorta looks like the kinda mech room you'd expect to see in an old haunted hotel! I expected to see Jack Nicholson peering around a corner...
That is one huge extank, ain't it?
(why does there have to be an ice storm of all days today?)

Just funnin' with ya Lucky... keep the pics coming!
#6
Member
Thread Starter
Looking at the gray floor standing tank I thought it was a well water supply update. But then seeing the size of the expansion tank on the ceiling, I'm thinking that the gray tank with the blue caps is the new expansion tank?
Looking forward to the final install pic's.
Al.
Looking forward to the final install pic's.
Al.
This would just be me, I wouldn't think of critiquing any sort of boiler install, but....
How the heck do you get to the power panels??? That can't be up to code..is it?
Was this some sort of commercial building? I'm sure there was another thread somewhere, but I don't normally look in the boiler section (unless there are pics to check out...lol)
How the heck do you get to the power panels??? That can't be up to code..is it?
Was this some sort of commercial building? I'm sure there was another thread somewhere, but I don't normally look in the boiler section (unless there are pics to check out...lol)

I am not sure if the expansion tank can legally be in front of the window (egress issue) but there is a door literally 6 inches from that window and you cant get to the window anyway with my dryer blocking it. So id have to think why would they worry about blocking a window that's already blocked by the dryer so i think the expansion tank should be ok. I never realized they can be on the floor either, thought they had to be hung. From all accounts Ill gain a decent amount of space with this change

and no this was always a house

BUT the coil was added later. There used to be an electric hot water tank here, i can see the electric for it.
#7
Member
Thread Starter
4 guys could barely move this out. The wheels on the handtruck looked like they would explode and now they are cleaning up the floor and all that (he said vermiculite?) that fell out. Hope it wasnt asbestos...cough cough. Then he asked me why I had no hot water to wash his hands 
















#9
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Good Pics
Lucky, thanks for the pics. Pretty good first installment.
I never even try to move those old boilers. It doesn't take long to section them. The sections can be hard enough to move, let alone the whole boiler.
If you don't know, ask your installer what is the purpose of that coil of copper near the flue pipe in the second picture. Never seen anything like it.
I never even try to move those old boilers. It doesn't take long to section them. The sections can be hard enough to move, let alone the whole boiler.
If you don't know, ask your installer what is the purpose of that coil of copper near the flue pipe in the second picture. Never seen anything like it.
#10
Member
Join Date: Aug 2006
Location: usa
Posts: 839
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I bet you a Beer 4U2 that it's some form of hammer arrestor.
LuckyD, if that new boiler and ODR setup doesn't save you a TON of $$$$ compared to that beast, I don't know what will. I hope you can report back in the future to give us some idea of the savings. If you can do K factor from your oil bills, that would be great.
Pete
#12
Member
Thread Starter
personally i thought the coil thing was an arrestor as mentioned above. But i heard him tell another guy it was a vent. So the truth may never be known
here's the end of day 1. Couldnt get a lot done because took a long time to clean up that 'greasy' mess all over the floor (per that dustpan pic above). Note the boiler was just put in from outside right before he left, not in final position. He had intended to use my newer circulator but couldnt find a gasket for it so i got a new one








here's the end of day 1. Couldnt get a lot done because took a long time to clean up that 'greasy' mess all over the floor (per that dustpan pic above). Note the boiler was just put in from outside right before he left, not in final position. He had intended to use my newer circulator but couldnt find a gasket for it so i got a new one









#13
Member
Thread Starter
#14
Hey, that boiler is way too small! The other one was 4 times as big...man are you gonna be cold ...LOL
Holy Crapola things have really changed haven't they?
Holy Crapola things have really changed haven't they?
#15
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Ain't it cute?
I guess when it got ripe & went from green to red, it shrunk.
Looks like the installer is using crimp on fittings on the copper. Makes a job go really fast but the fittings & tools are EXPENSIVE. You have to do a lot of copper fitting to justify the cost.
Looks like the installer is using crimp on fittings on the copper. Makes a job go really fast but the fittings & tools are EXPENSIVE. You have to do a lot of copper fitting to justify the cost.
#16
Member
Join Date: Jun 2008
Location: Rockville MD
Posts: 101
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I like that little boiler. It would have been my choice if I didn't go with the rebuild of my old one. I'd be interested to know what the noise difference is, with the higher speed burner and lack of shrouding.
#17
Member
Thread Starter
Oh yes it's fully mature now and shed the outer green skin. And i never saw crimped like this but i'm no plumber. He did tell me that the tools were very expensive....i think a few grand..or was that the pex tools? Well he definitely does a lot of work and pays attention to details and isn't cheap or taking the ez way out. At least that's all indications so far. He tossed in the 'free' new circulator in place of the one he thought he could re-use. Said his time wasnt worth finding a gasket.
#18
Member
Join Date: Aug 2006
Location: usa
Posts: 839
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Pro Press fittings. Looks good so far.
#19
Member
Thread Starter
--------------------
one question. The wiring for the 260 is a pain in my house (access issues/crawlspace). I thought i didnt get sun outside my one window next to the utility room even though it faces SW but now that the leaves have fallen, i see some sun does get there in winter. I 'think' the plan is to install the sensor on that SW wall (late afternoon sun) down between my tanks and that wall (it's an L shaped 'inner' corner at that point of the house). He will run the wiring out the same hole he has to drill for my new tigerloop setup.
i know the thing should be installed on north and so does he, but i'm not sure how possible that will be right now. He has to go in my attic to see if things could be dropped down that way to the north side. So is the winter sun really going to mess up the sensor if it does hit it? Ill try my best not to have it put there though. but maybe the tanks will block the sun

#21
Member
Thread Starter
look at post 12 the 2nd pic. He now wants to mount the board where the tekmar/emergency switch will go right under the stack pipe, next to the electrical box. What do you think of that. Initially he thought it would put it to the left of the hot water tank but now changed his mind. As you can see there's clearance to easily walk back there, totally around the boiler, but just wondering pros or cons of mounting it there vs near my water tank?
i guess less lines to run etc?
i guess less lines to run etc?
#22
Member
Thread Starter
piping done..now just waiting for the new oil line and hopefully the 260 install today..maybe into tomorrow even. And now my laundry room sink is mysteriously clogged. pressure is a trickle but all other faucets ok. Maybe some debris from the water line ?



#23
Man, that looks so much neater and more professionally laid out than the old one. I mean of course it should, right?
I'm no boiler guy...never really lived in an area that they were common. Did grow up in a house built in about 1890. Had a coal furnace "modernized" with an electric stoker(?). Guess they call that an octopus now? Man was our basement warm around that monster.
I'm no boiler guy...never really lived in an area that they were common. Did grow up in a house built in about 1890. Had a coal furnace "modernized" with an electric stoker(?). Guess they call that an octopus now? Man was our basement warm around that monster.
#24
Member
Thread Starter
hmm they started the new oil line and it's something bright and shiny (some kind of plastic?). I guess copper is expensive but was wondering is this common in the industry to use this new stuff? I guess with one nice long solid run vs all the joints it's safer though.
also talked to him about the outside sensor. He said he's going to hide it pretty well and even put in porches it's worked well. Of course ill monitor the outside temp to see if it's overshooting if it gets any direct sun.
also talked to him about the outside sensor. He said he's going to hide it pretty well and even put in porches it's worked well. Of course ill monitor the outside temp to see if it's overshooting if it gets any direct sun.
#26
Member
Thread Starter


edit: just heard it turn on for the first time. Doesnt seem too loud but the door is closed. Opened the door and tons of wiring yet to be done. I thought was near completion but i guess not after seeing wires everywhere lol. The 260 isnt even up on the board yet. Just playing with the burner and stat.
Last edited by luckydriver; 12-17-08 at 02:10 PM.
#28
Member
Thread Starter
Will post more pics tomorrow and he's coming back for a short time. Then ill ask him why this is SO loud when it starts. Scares the heck out of me as if bomb going off. Also i hear 'gurgling' but i dont think it's air..he said no air really in the system since the pipes stuck 5ft out of the floor. And he did bleed it thru the vent. But you can hear like rain tapping on a roof all thru the house in the baseboards and also from one of the pipes in the utility room. Like a tapping.
he did tell me it would run a lot tonight. But i imagine i even had a few short cycles. Oh well. will find out more then
#29
Member
Join Date: Dec 2007
Location: A Galaxy From Afar
Posts: 337
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If the next time is a bit longer delay the boom will only be louder...
Al.
#30
Member
Thread Starter
final pics will be posted in my next posting within the hour....sorry if any repeat shots..all the pics are newly taken but may show previous work.
He spent all morning today with me answering my silly questions. I understand what everything does but not what everything does...or rather why it does it
Hard to explain. I still dont understand how the cold gets back to the boiler..seems like it's all continually mixing!
also my old thermostat didnt play well with the boiler. Apparently it was calling for heat all night. No wonder went on ever 10 min or less. but it never got above 70 so that was good, he said that means he got the set up right. He replaced the thermostat with a nice new one..free! the loud booming was because he needed to adjust things more. Plus he said i get so much draft i probably should get a chimney cap. Apparently after it was short cycling so often it 'built up' or something like that and then boom.
From memory(i may get things out of place or wrong or misquote him, just warning you)
The aquastat is set at 160 or 170 high, i forget which. He may want to put a relay on it because as it stands now the tekmar starts the boiler and the circulator at the same time. With a time delay relay, when heat is called for the thing will circulate 1-10 min (depending on setting) and then use the residual heat in the boiler and only THEN will it fire up if it's needed.
Water temp is set at 137 and he played around and decided on a 16 differential (129 to 145). This was based on the performance overnight. The min water temp is set on 125 and max at 167. I'm very impressed the house was that warm with the 135 it was set at overnight. Even my cold room front of my house was warmer. More water circulating cooler (vs 180 in the old unit) but more often DOES keep you more comfortable. I'm living proof of it in only the 1st day of use. So any other newbies, this tekmar 260 IS worth it! I have 191 ft of baseboard and he estimated 100 gallons of water in there.
He has a firing delay of a minute vs keeping it on auto. I forget the reason now. I think to help it stop short cycling, which is why he choose the differential he did. We sat through MANY on/off cycles and he changed things many times. Not short cycling was important to him. the (co?) is 11.6% and he said he cant go above 12. this was in response to my complaints about the boom overnight.
Hot water is something i can play with. I understand about the mixing valve setting vs playing with the temp. he recommended keeping the tank at the factory half way point and if too hot, just turning down the mixing valve. He warned me if the water is too cold in the tank (ie i mentioned ill crank it all the way down), that the recovery may not be that quick. He said maybe 1/2 degree a day lost in the tank so keeping it hot wont be as costly as the old coil i had. My goal is just to avoid burning my hands like i did before with the 180 degree faucet water. He did show me in the manual all the temp settings so i can know what i'm doing
he said when hot water is being called for the heat circulator turns off for about 30 min max. Domestic has priority. I also saw all the shut off in line valves he put in and how you can just change out a single part without having to take down the entire system. Very well thought out and his partner said it was all put together as a test the previous night at his house.
It's 86.2 efficiency now and i have the little ticket it printed out with all the other info but i'm not home now to read all that off. he gave me the go ahead and play all i want with the settings...showed me how to work the board and if the differential isnt enough etc, go right ahead and change it. his goal was to give me longer cycles of heating up and cooling down vs short cycling. Also left tons of paperwork and manuals so Ill have some reading to do because I like to know what i got.
The only thing i'm not happy about is the (checkvalve)? On the pipe that feeds the house, that is supposed to stop the water from coming the other way. Well it 'rattles' and you can hear it if you are sitting in a quiet house...it is heard thru all the baseboards. I liken it to a loose ball bearing or that noise on your coffee maker just before it shuts off from boiling. He said he heard it but cant do anything about it? I know i'm supersensitive about new noises but anyone have any experiences where you can hear it throughout the baseboards?
He spent all morning today with me answering my silly questions. I understand what everything does but not what everything does...or rather why it does it

also my old thermostat didnt play well with the boiler. Apparently it was calling for heat all night. No wonder went on ever 10 min or less. but it never got above 70 so that was good, he said that means he got the set up right. He replaced the thermostat with a nice new one..free! the loud booming was because he needed to adjust things more. Plus he said i get so much draft i probably should get a chimney cap. Apparently after it was short cycling so often it 'built up' or something like that and then boom.
From memory(i may get things out of place or wrong or misquote him, just warning you)

The aquastat is set at 160 or 170 high, i forget which. He may want to put a relay on it because as it stands now the tekmar starts the boiler and the circulator at the same time. With a time delay relay, when heat is called for the thing will circulate 1-10 min (depending on setting) and then use the residual heat in the boiler and only THEN will it fire up if it's needed.
Water temp is set at 137 and he played around and decided on a 16 differential (129 to 145). This was based on the performance overnight. The min water temp is set on 125 and max at 167. I'm very impressed the house was that warm with the 135 it was set at overnight. Even my cold room front of my house was warmer. More water circulating cooler (vs 180 in the old unit) but more often DOES keep you more comfortable. I'm living proof of it in only the 1st day of use. So any other newbies, this tekmar 260 IS worth it! I have 191 ft of baseboard and he estimated 100 gallons of water in there.
He has a firing delay of a minute vs keeping it on auto. I forget the reason now. I think to help it stop short cycling, which is why he choose the differential he did. We sat through MANY on/off cycles and he changed things many times. Not short cycling was important to him. the (co?) is 11.6% and he said he cant go above 12. this was in response to my complaints about the boom overnight.
Hot water is something i can play with. I understand about the mixing valve setting vs playing with the temp. he recommended keeping the tank at the factory half way point and if too hot, just turning down the mixing valve. He warned me if the water is too cold in the tank (ie i mentioned ill crank it all the way down), that the recovery may not be that quick. He said maybe 1/2 degree a day lost in the tank so keeping it hot wont be as costly as the old coil i had. My goal is just to avoid burning my hands like i did before with the 180 degree faucet water. He did show me in the manual all the temp settings so i can know what i'm doing
he said when hot water is being called for the heat circulator turns off for about 30 min max. Domestic has priority. I also saw all the shut off in line valves he put in and how you can just change out a single part without having to take down the entire system. Very well thought out and his partner said it was all put together as a test the previous night at his house.
It's 86.2 efficiency now and i have the little ticket it printed out with all the other info but i'm not home now to read all that off. he gave me the go ahead and play all i want with the settings...showed me how to work the board and if the differential isnt enough etc, go right ahead and change it. his goal was to give me longer cycles of heating up and cooling down vs short cycling. Also left tons of paperwork and manuals so Ill have some reading to do because I like to know what i got.
The only thing i'm not happy about is the (checkvalve)? On the pipe that feeds the house, that is supposed to stop the water from coming the other way. Well it 'rattles' and you can hear it if you are sitting in a quiet house...it is heard thru all the baseboards. I liken it to a loose ball bearing or that noise on your coffee maker just before it shuts off from boiling. He said he heard it but cant do anything about it? I know i'm supersensitive about new noises but anyone have any experiences where you can hear it throughout the baseboards?
Last edited by luckydriver; 12-18-08 at 11:25 AM.
#31
Member
Join Date: Aug 2006
Location: usa
Posts: 839
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'd like to know more about his Tekmar settings. The Tekmar should determine the best differential and control short cycling, but I've been fiddling with mine doing some of the same things for the same reasons. (Going to a fixed differential, etc.) The firing delay is interesting... I wonder if that also gets the water circulating before the burner fires? Something to check. It sounds like your guy really cares about his work and making things right!!!
#32
Member
Thread Starter
#34
Member
Thread Starter
before i forget
THANK YOU to all those that sat through my tortuous questions. I may not always understand but i do try my hardest to soak up the knowledge Beer 4U2
He did tell me that the 260 usually does control that diff and that it takes 2 weeks to learn things, but maybe because I told him it was turning on ever few min or so that he figured it wasnt the 'best' it could be and did the manual setting. Also i think he said the 'boom' i heard was from too much short cycling.
the firing delay doesnt mean the circ. comes on first. He said he needs another relay on the aquastat so that when it calls for heat, it will first turn on the circ. THEN if after the 1-10 min (user programmed) it still needs heat, it will fire. He said right now the burner and the circulator are tied together and are on and off at the same time. But maybe if running a minute prevents the burner from coming on too soon, more savings can be achieved.
fire delay is this per the manual:
The Fire Delay is the delay time that occurs between the time that the 260 closes the Boiler contact and the burner fires. This delay is usually the result of burner pre-purge, or other forms of time delay built into the burner’s safety circuits
I pretty sure he put that in to help stop any short cycling
THANK YOU to all those that sat through my tortuous questions. I may not always understand but i do try my hardest to soak up the knowledge Beer 4U2
I'd like to know more about his Tekmar settings. The Tekmar should determine the best differential and control short cycling, but I've been fiddling with mine doing some of the same things for the same reasons. (Going to a fixed differential, etc.) The firing delay is interesting... I wonder if that also gets the water circulating before the burner fires? Something to check. It sounds like your guy really cares about his work and making things right!!!
the firing delay doesnt mean the circ. comes on first. He said he needs another relay on the aquastat so that when it calls for heat, it will first turn on the circ. THEN if after the 1-10 min (user programmed) it still needs heat, it will fire. He said right now the burner and the circulator are tied together and are on and off at the same time. But maybe if running a minute prevents the burner from coming on too soon, more savings can be achieved.
fire delay is this per the manual:
The Fire Delay is the delay time that occurs between the time that the 260 closes the Boiler contact and the burner fires. This delay is usually the result of burner pre-purge, or other forms of time delay built into the burner’s safety circuits
I pretty sure he put that in to help stop any short cycling
#35
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
This reads as if you got a really good install. I am especially impressed at how your installer has worked at getting your boiler and ODR to work. I'm thinking that you definitely got your money's worth from this guy although there are a few little nit-picky things I would have done differently.
#36
Member
Thread Starter
found my 'receipts' and i guess these numbers mean something to you guys..not me 
initial firing
Ex/A 33.9
O2 5.3%
CO 58ppm
Coaf 77ppm
CO2 11.7
DRFT -.04 IN H2O
AT 59.1F
FINAL
Ex/A 35.4%
02 5.5%
FT 386.1 f
CO 55PPM
EFF 86.2%
COaf 74PPM
CO2 11.6%
DRFT -.04 IN H20
AT 65.9f

initial firing
Ex/A 33.9
O2 5.3%
CO 58ppm
Coaf 77ppm
CO2 11.7
DRFT -.04 IN H2O
AT 59.1F
FINAL
Ex/A 35.4%
02 5.5%
FT 386.1 f
CO 55PPM
EFF 86.2%
COaf 74PPM
CO2 11.6%
DRFT -.04 IN H20
AT 65.9f
#37
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Sure do! I can't speak to the actual numbers because I have no hands-on experience with these little baby boilers but I'll tell you what the abbreviations are and what they mean. (my comments in blue.)
found my 'receipts' and i guess these numbers mean something to you guys..not me 
initial firing
Ex/A 33.9 Excess air in the exhaust gases, the amount of air over the theoretical minimum for perfect combustion.
O2 5.3% Oxygen content in the exhaust gases. Less is better.
CO 58ppm Carbon Monoxide in the exhaust gases. Less is better.
Coaf 77ppm This one I don't know. It could be the CO adjusted for interfering gases.
CO2 11.7 Carbon Dioxide in the stack gases, higher is better.
DRFT -.04 IN H2O Draft measured in inches of water column. Could be measured at breeching (boiler exhaust outlet) or overfire (in combustion chamber) Reading depends upon manufacturer's recommendation.
AT 59.1F Ambient temperature, the temperature of the air in the boiler room.
FINAL
Ex/A 35.4%
02 5.5%
FT 386.1 f
CO 55PPM
EFF 86.2%
COaf 74PPM
CO2 11.6%
DRFT -.04 IN H20
AT 65.9f

initial firing
Ex/A 33.9 Excess air in the exhaust gases, the amount of air over the theoretical minimum for perfect combustion.
O2 5.3% Oxygen content in the exhaust gases. Less is better.
CO 58ppm Carbon Monoxide in the exhaust gases. Less is better.
Coaf 77ppm This one I don't know. It could be the CO adjusted for interfering gases.
CO2 11.7 Carbon Dioxide in the stack gases, higher is better.
DRFT -.04 IN H2O Draft measured in inches of water column. Could be measured at breeching (boiler exhaust outlet) or overfire (in combustion chamber) Reading depends upon manufacturer's recommendation.
AT 59.1F Ambient temperature, the temperature of the air in the boiler room.
FINAL
Ex/A 35.4%
02 5.5%
FT 386.1 f
CO 55PPM
EFF 86.2%
COaf 74PPM
CO2 11.6%
DRFT -.04 IN H20
AT 65.9f
#39
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
COaf
CO(af) stands for carbon monoxide (air free). This is a calculation of what the CO would be if there were no excess air in the flue gases. The 77 ppm is well below the "100 ppm max." generally accecpted limit.
#40
Member
Thread Starter

So I still have the same 60 yr old 'water' that was in the house originally i guess. I know when i have bled the baseboards it always looked like straight water and i never smelled or saw anything that indicated any antifreeze. But i'm not gonna taste it to be sure.
I'm glad to hear everyone say he did this right. For that amount of money i was hoping he would and my gut about him being anal about things was right.
i'm sitting here in bare feet (normally my feet are freezing) and the new 67 degrees does feel warmer than the old that i had with the other unit.