oil boiler transformer failure -repeated
#1
Member
Thread Starter
Join Date: Jan 2009
Location: New York
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
oil boiler transformer failure -repeated
I have an older oil burner (Carlin) and boiler which I bought used 6 years ago. The transformer that was on the unit worked fine until last February. It failed an I replaced it with a new transformer sold to me by my local plumbing supply store as an appropriate replacement (a Dongan XD-CR205). That transformer failed after approximately four months of use (boiler not used over summer) and was replaced on 10-27-08. Today (1-10-09), the replacement transformer failed after just over two months of use. These things cost almost 50 bucks a pop and I'd like to know what could be causing these failures.
I've run oil burners for nearly 20 years and never had a transformer fail before.
psolbeny
I've run oil burners for nearly 20 years and never had a transformer fail before.
psolbeny
#3
Do you have any excessive heat coming from the burner area? Check the overfire draft of the boiler with a draft gauge. If pressure firing, it could cause excessive heat relating to premature failure of the transformer.
#4
Member
Thread Starter
Join Date: Jan 2009
Location: New York
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
More help needed
Thanks!
Psolbeny
#5
I guess another thing you can check yourself is to make sure the incoming voltage is at 120vac. If the voltage is spiking or lower than 80% of normal, it would also cause the transformer to act up or burn out.