any one know the proper way to wire a wiel mclain boiler to a three wire white rodgers zone valves with thre wire thermostats also have a honeywell 2 wire for the water heater it had 2 transformers the first time but it shorted out one of them when we installed the new valves

#3
Member
Thread Starter
Join Date: Jan 2009
Location: midwest
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts

#4
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
check out this schematic for that valve http://www.white-rodgers.com/wrdhom/.../0037-2304.pdf
#6
Mike, how many zones are you wiring? You will use one 40 VA transformer for every 4 valves.
I did this drawing for another poster a while back, and it shows the hookup for 2 valves. The T T wires are the ones that would go to the Y G on the boiler control.
One note I'd like to add:
On those zone valves, terminals 2 and 5 are the same point, they are connected internally on the zone valve.
Let me know if any questions...
I did this drawing for another poster a while back, and it shows the hookup for 2 valves. The T T wires are the ones that would go to the Y G on the boiler control.
One note I'd like to add:
On those zone valves, terminals 2 and 5 are the same point, they are connected internally on the zone valve.
Let me know if any questions...

#7
Member
Thread Starter
Join Date: Jan 2009
Location: midwest
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
CGI wiring diagram
my only question is that if i unhook everything except for the boiler control i have 24 volts between y and g so do i need a second transformer for the zone valves or will it be ok with just one? there is two zones for heating and one for hot water but the hot water is a honeywell 2 wire valve im getting thrown off with the transformer placement and 24 volts at the y and g sorry if this sounds confusing but im great with standard two wire setups it just the three wire set up is confusing to me
my only question is that if i unhook everything except for the boiler control i have 24 volts between y and g so do i need a second transformer for the zone valves or will it be ok with just one? there is two zones for heating and one for hot water but the hot water is a honeywell 2 wire valve im getting thrown off with the transformer placement and 24 volts at the y and g sorry if this sounds confusing but im great with standard two wire setups it just the three wire set up is confusing to me

Last edited by NJT; 01-25-09 at 04:23 PM.
#8
You WILL see 24VAC on the open Y and G terminals... or almost any other aquastat for that matter. That's normal... BUT:
It does NOT mean that you can power zone valves from that source. SOME aquastats CAN power zone valves... but that control in your boiler can NOT. Don't even try!
You need one external transformer. I can add the Honeywell valve to the drawing to show ya how to hook that up along with the other two. One 40 VA transformer will work for two 1311's and one 8043 ...
Mike, which Honeywell valve? Terminal screws? or RED / YELLOW lead wires?
It does NOT mean that you can power zone valves from that source. SOME aquastats CAN power zone valves... but that control in your boiler can NOT. Don't even try!
You need one external transformer. I can add the Honeywell valve to the drawing to show ya how to hook that up along with the other two. One 40 VA transformer will work for two 1311's and one 8043 ...
Mike, which Honeywell valve? Terminal screws? or RED / YELLOW lead wires?
#10
If when you say you need two transformers, you mean the one in the control in the boiler, and another one outside to power the valves, yes...