help with weil mclain boiler with w/r 3 wire zone valve


  #1  
Old 01-24-09, 06:17 PM
M
Member
Thread Starter
Join Date: Jan 2009
Location: midwest
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Angry help with weil mclain boiler with w/r 3 wire zone valve

any one know the proper way to wire a wiel mclain boiler to a three wire white rodgers zone valves with thre wire thermostats also have a honeywell 2 wire for the water heater it had 2 transformers the first time but it shorted out one of them when we installed the new valves
 
  #2  
Old 01-24-09, 07:02 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Mike, I'm sure someone does!

Give us the model numbers of the valves... thermostats, etc ...

Tell us in more detail what you are trying to do.
 
  #3  
Old 01-25-09, 08:37 AM
M
Member
Thread Starter
Join Date: Jan 2009
Location: midwest
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
the zone valves are white rodger 1311 zone valves the thermostats are compatable type for the 3 wire system the model on the boiler still working on but it is a weil mclain boiler about 8 years old the boiler control that operates the pump and the gas valve is just a standard fan control center that has two wires coming from y and g terminals when we wired it up the first time the valve would operate but the boiler would not fire where trying to do this with just one transformer but if needed i can install 2
 
  #4  
Old 01-25-09, 09:11 AM
S
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes on 0 Posts
check out this schematic for that valve http://www.white-rodgers.com/wrdhom/.../0037-2304.pdf
 
  #5  
Old 01-25-09, 10:00 AM
M
Member
Thread Starter
Join Date: Jan 2009
Location: midwest
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
the boiler model is i beleave is a CGI-1 it shows that y ang g are normally to the thermostat so how can i wire this into the system ?
 
  #6  
Old 01-25-09, 10:44 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Mike, how many zones are you wiring? You will use one 40 VA transformer for every 4 valves.

I did this drawing for another poster a while back, and it shows the hookup for 2 valves. The T T wires are the ones that would go to the Y G on the boiler control.

One note I'd like to add:

On those zone valves, terminals 2 and 5 are the same point, they are connected internally on the zone valve.

Let me know if any questions...

 
  #7  
Old 01-25-09, 12:55 PM
M
Member
Thread Starter
Join Date: Jan 2009
Location: midwest
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
CGI wiring diagram

my only question is that if i unhook everything except for the boiler control i have 24 volts between y and g so do i need a second transformer for the zone valves or will it be ok with just one? there is two zones for heating and one for hot water but the hot water is a honeywell 2 wire valve im getting thrown off with the transformer placement and 24 volts at the y and g sorry if this sounds confusing but im great with standard two wire setups it just the three wire set up is confusing to me
 

Last edited by NJT; 01-25-09 at 04:23 PM.
  #8  
Old 01-25-09, 04:29 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
You WILL see 24VAC on the open Y and G terminals... or almost any other aquastat for that matter. That's normal... BUT:

It does NOT mean that you can power zone valves from that source. SOME aquastats CAN power zone valves... but that control in your boiler can NOT. Don't even try!

You need one external transformer. I can add the Honeywell valve to the drawing to show ya how to hook that up along with the other two. One 40 VA transformer will work for two 1311's and one 8043 ...

Mike, which Honeywell valve? Terminal screws? or RED / YELLOW lead wires?
 
  #9  
Old 01-25-09, 06:05 PM
M
Member
Thread Starter
Join Date: Jan 2009
Location: midwest
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Smile

thats what i thought is i need two transformers the honeywell is red yellow leads
 
  #10  
Old 01-25-09, 06:51 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
If when you say you need two transformers, you mean the one in the control in the boiler, and another one outside to power the valves, yes...

 

Last edited by NJT; 01-25-09 at 07:29 PM.
  #11  
Old 01-25-09, 06:54 PM
M
Member
Thread Starter
Join Date: Jan 2009
Location: midwest
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Smile

thanks for clearing that up i really am thankfull for your help
 
 