Leaking Pressure/Temperature Relief Valve
Hello,
I just purchased a home with a natural gas water baseboard heat system. Since I've moved in the home, it's been my opinion that the boiler cycles on and off too often.
I noticed some operating parameters that seem out of the ordinary. According to the temperature/pressure gauge on the pipe label labeled "to system", the boiler cycle between 140ºF and 170ºF; the flame ignites at 140ºF and turns off at 170ºF. The pressure needle on the guage does not work... it's reading below zero PSI. The problem I noticed is that once the temperature reaches about 150ºF, the pressure/temperature relief valve on the top of the boiler tank begins to leak. I'm assuming this is not normal operation, correct?
The unit is a Weil-McLain Gold GV. It was installed in 1993. How long do units such as this one usually last?
This is what the unit looks like:

Thanks,
Rich
I just purchased a home with a natural gas water baseboard heat system. Since I've moved in the home, it's been my opinion that the boiler cycles on and off too often.
I noticed some operating parameters that seem out of the ordinary. According to the temperature/pressure gauge on the pipe label labeled "to system", the boiler cycle between 140ºF and 170ºF; the flame ignites at 140ºF and turns off at 170ºF. The pressure needle on the guage does not work... it's reading below zero PSI. The problem I noticed is that once the temperature reaches about 150ºF, the pressure/temperature relief valve on the top of the boiler tank begins to leak. I'm assuming this is not normal operation, correct?
The unit is a Weil-McLain Gold GV. It was installed in 1993. How long do units such as this one usually last?
This is what the unit looks like:

Thanks,
Rich
#2
Rich, first things first, you've gotta know the pressure in the system. So, you've either gotta replace the gauge, or improvise an 'external' pressure gauge. I always post this pic of my junque boxe model, but nicer ones can be made... or bought...

Screw this thing onto a drain, open it, and read the pressure.
Does your home have a separate hot water heater? or does the hot water come from the boiler?
If you feel adventurous, see that gray box on the side of the boiler? That's your 'aquastat'. There should be one small screw holding the cover on. Turn the emergency switch to the boiler off, loosen that screw and slide the cover off. There should be a label inside... what is the model # of that box?
Next, what type of 'expansion tank' do you have? Is it the type that looks like a gas tank from a grill? or is it a bigger steel one that's strapped into the ceiling joists above the boiler?

Screw this thing onto a drain, open it, and read the pressure.
Does your home have a separate hot water heater? or does the hot water come from the boiler?
If you feel adventurous, see that gray box on the side of the boiler? That's your 'aquastat'. There should be one small screw holding the cover on. Turn the emergency switch to the boiler off, loosen that screw and slide the cover off. There should be a label inside... what is the model # of that box?
Next, what type of 'expansion tank' do you have? Is it the type that looks like a gas tank from a grill? or is it a bigger steel one that's strapped into the ceiling joists above the boiler?
#3
Member
Thread Starter
Join Date: Feb 2009
Location: Grosse Ile, Michigan
Posts: 116
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks NJ Trooper!
I'll get a new pressure guage soon, but for now I'll try to rig something up this weekend.
I just wanted to provide a little more information about the system.
The hot water tank is fed from the boiler. It's a Amtrol WH-7.
The backflow preventer is a No9D.
The reducing valve is a ITT Bell & Gossett model B7-12. (I think... there's a scratch on the label and I'm not positive it's a 7 in the model #.)
The expansion tank is of the propane tank looking variety. It's a Amtrol Extrol model #30.
If I'm looking at what you're referring to as the 'aquastat', I don't think that's it. That is just a metal j-box where the 110v power comes to the boiler unit. Between the 110v power switch and that gray box, there is a black box labeled "McDonnell Level Control - ITT McDonnell & Miller." The flexible conduit runs to this box from the shutoff switch and then to the gray j-box mounted to the side of the boiler housing. The "from system" water line also runs to this box. Is this the aquastat?
Thanks again for your help.
I'll get a new pressure guage soon, but for now I'll try to rig something up this weekend.
I just wanted to provide a little more information about the system.
The hot water tank is fed from the boiler. It's a Amtrol WH-7.
The backflow preventer is a No9D.
The reducing valve is a ITT Bell & Gossett model B7-12. (I think... there's a scratch on the label and I'm not positive it's a 7 in the model #.)
The expansion tank is of the propane tank looking variety. It's a Amtrol Extrol model #30.
If I'm looking at what you're referring to as the 'aquastat', I don't think that's it. That is just a metal j-box where the 110v power comes to the boiler unit. Between the 110v power switch and that gray box, there is a black box labeled "McDonnell Level Control - ITT McDonnell & Miller." The flexible conduit runs to this box from the shutoff switch and then to the gray j-box mounted to the side of the boiler housing. The "from system" water line also runs to this box. Is this the aquastat?
Thanks again for your help.
#4
I just re-acquainted myself with your boiler... can you tell the 'series' number of the boiler? What's it say on the ID plate? You don't have the 'aquastat' I mentioned... there's a 'control module' in that boiler.
Offhand, it sounds as though your expansion tank is either very low on air, or has a ruptured bladder. When the water hits 150 degrees, the pressure is up around 30, and the relief valve opens.
Is there a shutoff valve in the line between the boiler and the expansion tank? or is it piped directly?
You need to shut off the boiler, close the manual feedwater valve, and open a drain on the boiler to get the system pressure to ZERO (but you won't know till you get a gauge!), and using an accurate tire pressure gauge on the tank air fitting, check to see that you have 12-15 PSI air charge. If the tank air fitting is pointing DOWN, and you get WATER out of that air valve, you need a new tank. If you don't get water, use a bicycle pump or small air compressor and put 15 PSI in the tank. Then, reopen the manual valve and repressurize the system. Turn the boiler back on and you should be good to go.
NOTE! Do NOT drain any more water than you need to in order to drop the pressure to zero. The less water you change, the better.
Offhand, it sounds as though your expansion tank is either very low on air, or has a ruptured bladder. When the water hits 150 degrees, the pressure is up around 30, and the relief valve opens.
Is there a shutoff valve in the line between the boiler and the expansion tank? or is it piped directly?
You need to shut off the boiler, close the manual feedwater valve, and open a drain on the boiler to get the system pressure to ZERO (but you won't know till you get a gauge!), and using an accurate tire pressure gauge on the tank air fitting, check to see that you have 12-15 PSI air charge. If the tank air fitting is pointing DOWN, and you get WATER out of that air valve, you need a new tank. If you don't get water, use a bicycle pump or small air compressor and put 15 PSI in the tank. Then, reopen the manual valve and repressurize the system. Turn the boiler back on and you should be good to go.
NOTE! Do NOT drain any more water than you need to in order to drop the pressure to zero. The less water you change, the better.
#6
Member
Thread Starter
Join Date: Feb 2009
Location: Grosse Ile, Michigan
Posts: 116
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks... I would really like to get fairly familliar with this system, so I apologize for the numerous questions. I was kind of wondering why the hot water tank says "Residential Hot Water Maker" on it when it doesn't really "make" any hot water... isn't it just more of a storage tank? Is an indirect water heater generally preferred over a standalone water heater? It seems it has some advantages, but one disadvantage is that I can't take the whole system down and still take a hot shower. 
The boiler is a model GU-4 Series 2.
There is a shutoff valve and a drain valve. The expansion tank is connected to and suspended by the pipe above it with the schraeder valve on the bottom.
Is this the valve that supplys the system with city water?
How will I know it's safe to unthread the current broken gauge w/o knowing the pressure in the system? Shall I drain it a bit and then just unthread the gauge slowly and carefully?
Is the reason for this just so the system only has to reheat as little new water as possible or are there other reasons that you don't want to introduce a lot of new water to the system? I just bought this house and I'm not really sure how long it's been leaking, but by the looks of the concrete around the boiler, it's been a while... that leads me to believe that it's efficiency is being severely compromised because of all the wasted hot water.
Also, I know nothing about the name brands I'm dealing with... i.e. Weil McLain, Amtrol, ITT, etc... Are these reputable brands and how do they rank overall? Are they like a Yugo or a Bentley?
I took a bunch of pictures of the system, but unfortunately I just moved in to this house and can't find the cable for my camera!
Thanks again,
Rich

Originally Posted by NJ Trooper
... can you tell the 'series' number of the boiler? What's it say on the ID plate?
Originally Posted by NJ Trooer
Is there a shutoff valve in the line between the boiler and the expansion tank? or is it piped directly?
Originally Posted by NJ Trooper
...close the manual feedwater valve...
Originally Posted by NJ Trooper
...and open a drain on the boiler to get the system pressure to ZERO (but you won't know till you get a gauge!)
Originally Posted by NJ Trooper
NOTE! Do NOT drain any more water than you need to in order to drop the pressure to zero. The less water you change, the better.
Also, I know nothing about the name brands I'm dealing with... i.e. Weil McLain, Amtrol, ITT, etc... Are these reputable brands and how do they rank overall? Are they like a Yugo or a Bentley?
I took a bunch of pictures of the system, but unfortunately I just moved in to this house and can't find the cable for my camera!

Thanks again,
Rich
#7
isn't it just more of a storage tank? Is an indirect water heater generally preferred over a standalone water heater?
The boiler is a model GU-4 Series 2.
That's an 'older' one then... I believe that your boiler has one pump internally, and also a 'mixing valve'... the series 3 and newer have replaced the mixing valve with a second pump. You can download the manual from the Weil-Mclain website if you don't have it.
There is a shutoff valve and a drain valve.
Is this the valve that supplys the system with city water?
How will I know it's safe to unthread the current broken gauge w/o knowing the pressure in the system? Shall I drain it a bit and then just unthread the gauge slowly and carefully?
Is the reason for this just so the system only has to reheat as little new water as possible or are there other reasons that you don't want to introduce a lot of new water to the system?
A long term leak will constantly add oxygen to the system and will cause faster corrosion to the parts... also, minerals in the water will build up inside.
Hunt down that cable... so much easier with pics so we can tell you which valves to turn...
#8
Member
Thread Starter
Join Date: Feb 2009
Location: Grosse Ile, Michigan
Posts: 116
Upvotes: 0
Received 0 Upvotes
on
0 Posts

That's an overall photo of the system, and I think the link below should take you to the album w/ more detailed photos.
Boiler pictures by bajafx4 - Photobucket
#9
Member
Thread Starter
Join Date: Feb 2009
Location: Grosse Ile, Michigan
Posts: 116
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Originally Posted by NJ Trooper
It is a storage tank. There is a coil of pipe inside through which the boiler water passes and heats the water in the tank.
Originally Posted by NJ Trooper
Is the drain valve in between the tank and the shutoff valve?
We're going to a birthday party right now and my wife is waiting at the door for me. HA! Or else I go down and check to see if that model number is GU or GV. I do remember for sure that there's a company label on the boiler from the installer that says they installed the system in 1993 if that helps.
Gotta go,
Rich
#10
Rich, there's no drain or valve that I can see between the system and the expansion tank. What I meant was something like this:

Setup like this, and you can isolate the expansion tank and drain the pressure from only the tank. Otherwise, you still have to relieve the pressure from your system as I first described.
4 pipes into water heater:
Yes, the water heater is for all intents another 'zone' on the heating system. When it cools, the control on the water heater calls the boiler just as a zone thermostat would do.
BTW, I added a few comments to your pics...

Setup like this, and you can isolate the expansion tank and drain the pressure from only the tank. Otherwise, you still have to relieve the pressure from your system as I first described.
4 pipes into water heater:
Yes, the water heater is for all intents another 'zone' on the heating system. When it cools, the control on the water heater calls the boiler just as a zone thermostat would do.
BTW, I added a few comments to your pics...