New boiloer install questions
Received 0 Votes
Going to install a new boiler system. Have a 35 year old WM with 3 zones (with zone valves).
Putting in new Burnham MPO with a super store indirect heater. Questions?
Is there an advantage to using zone valves or putting in circulators?
Should the system circulator be placed on the return or supply side? Which is better?
My boiler is in the garage and the boiler is at one end (where the oil line comes in) and the zone valves are on the other end. Would it be better to put the indirect heater on the side closer to the boiler or on the other side closer to the zone valves?
Do I need a separate circulator for the indirect heater? If so how is that wired up?
Thanks for any help!!!
If you have a single circulator and it fails you have no heat at all in the house whereas if you have multiple circulators and one fails you will have heat in the other zones. Although it will add to the cost, I recommend isolation valves on any circulator to enable changing of the circulator without having to drain the system.
Received 0 Votes
Here's the directions. Follow all of them.
http://burnham.com/PDF/IO/MPO.pdf
I suggest Figure 18A for water piping.
Received 0 Votes
Because I would have bought a couple Wilo ECO's and just stuck them in there. Simple. No need to change any piping, control, relays, etc. etc. Payback on a simple swap would be 4 yr. (Electricity is 23 cents/kWh here). Adding new external flowchecks (e.g., B&G checktrol or Taco Swet-chek) lengthens it quite a bit. Plus everything fits quite nicely as is.
Received 0 Votes
circulator sizing?
So I am now leaning towards the Taco Circ with FC instead of going with zone valves.
My zones are as follows
1 has a length of about 20 feet
2 has about 80 feet
3 has about 100 feet
and 4 is the indirect water heater (Superstor Ultra) 45 gallon which states a flow rate of 10 and pressure drop of 7.9.
What would be the best sizes of circs for these (Taco 007)?
Also, what is "head range" refer to?
Thanks
2 has about 80 feet
Thanks
Received 0 Votes
Oh if it were only that easy....
The real way to figure the proper circulator size is here:
http://www.taco-hvac.com/uploads/Fil...irculators.pdf
Doesn't take too long.
The shortcut is to just use a 007 for each zone and live with some overpumping of short zones. Some of the smaller sizes can be hard to find. The 007 is ubiquitous.
Ordinarily I would say for a 3-zone system to go with zone valves and a single ECM variable speed circulator, OR zone valves and something like a 007 plus a pressure differential bypass valve. But in Fairbanks (where ASHRAE says the outdoor design temperature is -47F), having a bunch of circs pumping water is probably a good thing. One goes down you can still run the others or even move one to another zone. Of course, if you go single circ then you could also just keep a spare or two on the shelf....
For whatever circs you choose, use some nice isolation flanges, such as these: http://www.taco-hvac.com/uploads/Fil...ry/101-101.pdf
For the indirect, you could do a Taco 00R 3-speed on medium,
http://www.taco-hvac.com/uploads/FileLibrary/100-51.pdf
or a 007.
or a 007.
Received 0 Votes
You would place it at the end of the supply manifold (after the last zone valve) and tie it into the return manifold. If your manifolds are close to each other, this is a simple, short piping run.
Can't think of a good diagram that shows a PDBV piped to a standard boiler, but here's a diagram for essentially the same application (adjacent supply/return manifolds with zone valves) for a different boiler:
http://www.htproducts.com/literature/lp-185.pdf
Figure 2B on page 23.
Received 0 Votes
OK, that looks simple since my manifolds are close by each other. Thanks. So now I am thinking I am going to go ahead and do the zone valves with a 007 system circulator. I think I will buy another just to have on hand. Don't want to be like last year and hit -60 and have mine go out at 2 AM.
Thanks!
Also, on a side note. I keep seeing these vented on the manual through a chimney. I don't have a chimney on my current boiler, just the pipe going straight up through the ceiling. Any problems with this?
Thanks!
Received 0 Votes
zone circs
I NEVER use a circulator on every zone. It uses a lot more power. Also, I usually have more than 3 zones so the extra cost adds up. I just don't see an advantage of a bunch of circs, especially if you already have a boiler set up with zones. I would not even consider the extra work and expense. We have thousands of boilers here in Fairbanks with one circ, including huge houses, including 3 stories and have never had a lack of circ with the standard circ pump that comes with the boiler. The MPO is very popular here btw.
I don't put a separate pump on the domestic tank either, simply another zone valve wired with all the rest. Easy.
I usually put about 6 zones in a house. If you have a boiler, why not enjoy the savings of lots of zones.
How often do you see a failed main circulator? Very rare. My house, the circ is 25 yrs old! It is on the 1st System 2000 in the state.
Also very dependable, are the Honeywell zone valves that spring closed. It is a simple low voltage circuit from t-stat, to zv to 24v transformer to open the zone. The red end zone pair bundle and goes to the boiler TT.
A bunch of zones????? Micro zoning is never a good thing. You are worried about the use of power from small circulators and then micro-zone so the boiler short cycles and decreases the efficiency. It may be wasting more fuel that way then a bunch of wet rotor circulators would be wasting electric. Everything has limits. If you want to be Green, Keep zoning to a minimum, use zone valves, properly size the boiler, proper near boiler piping, DPBV, and combustion test to complete the job.
Received 0 Votes
Thanks Bilbo
What you are saying is what I thought at first but then as I got further into this install and started reading other ideas I wasn't sure what was best or not.
I am going to be doing this install when I get back home in early Sept. Thanks for the offer, I may take you up on it.
Received 0 Votes
I am wondering now, what would be the easiest thermostats to install?
I would like to have a programmable model but I know I replaced one about a year ago and had a heck of a time trying to wire it to the existing 2-wire system. Somehow I got it hooked up and it works but I was wondering if there may be a certain model that would be better for a 2-wire system?
Thanks.
Thanks.
Received 0 Votes
Alaskanstar- I am in the book: KevinCorr. I am putting in an MPO next week.
Rbeck- I disagree. I have read research that indicates that not heating areas of the house that you are not using saves energy.
Studies show that you can save up to 18% that way.
When I first sold System 2000 the system manager was set up for 4 zones. They use spring shut, power on Honeywell ZV. They quickly changed it to 5 zones standard, and made a diagram for combining two managers for 10 zones. I don't work with it now, but I think they have made that into one optional big manager.
You can call or email them if you want some evidence.
Received 0 Votes
Hi Alaskastar and Bilbo,
I enjoyed reading your emails. I have a new question. I like to run it by you because you seem to be very knowlegeable on boilers and controls.
Last week, I replaced a 45 year old HydroTherm hot water gas fired boiler with a new HydroTherm HW 100-8, 175K BTU/hr unit (single circulator). The 4 tstats and 4 Honeywell zv's are existing. The new boiler comes with a control center. The control center has a 24V step down transformer. We completed all the piping, gas line and flue duct. We jumped across the tstat terminals in the control center to test, the boiler fired up nicely. Now we are ready to hook up the electrical.
The control center in the new boiler has a 24V AC stepdown transformer. I believe this new 24V AC source can power up all the thermostats and zone valves in the system. The thermostat wiring shown in the diagram is for only one tstat only. There is no example diagram on tie-ins with zv's. My old control had one 24V transformer and one Honeywell RA832A controller (two separate pieces). The Honeywell 832A activates the circulator and opens the gas valve. What will be the easiest way to re-wire the tstats and zv's for this new boiler?
Thanks,
plin1
Thanks,
plin1
#21
If the boiler has a certain output and has many smaller zones the AFUE efficiency will absolutely be affected. If a zone of 1/5th the total input the boiler will short cycle. The boiler needs to run 5-7 minutes to hit peak efficiency. If short cycling does not affect efficiency and fuel consumption why do we properly size boilers, install modulating boilers and use buffer tanks?
There are more than one manufacturer that will disagree with the theory of saving fuel by not heating areas. The interior walls are not insulated. For example, heat a dinning room to 70f. The bedroom on the other side of the dinning room wall is 65f. The wall in the dinning room will cool quicker causing the room to cool down quicker and the thermostat will call quicker. Some homeowners today go to extremes and will try to set the setback thermostat in the bedroom area down as low as 10f. Not the bedroom is 60f and the dinning room is 70f. The cool down is even more than before.
Siggy proved mathematically that cast iron has about the best thermal transfer of any product which also is different than one company states.
#22
Received 0 Votes
I am not a wiring or electric or electronic expert, just a pipefitter, plumber who has been forced to learn enough to install boilers.
All that I would say about wiring Honeywll zone valves is that if you have honeywell spring closed zone valves, that the 24 volt circuit loop from the transformer to the zv motor yellow and orange to the the thermostat and back to the transformer is a simple circle that does not go to the boiler. The zv end switch has two red wires which you jump to the next zone valve and send one pair to the boiler TT.
#23
Received 0 Votes
rbeck- "...Siggy proved mathematically that cast iron has about the best thermal transfer of any product which also is different than one company states..."
Some boilers are made of steel instead of cast iron NOT for thermal transfer but for durability and flexibility for a low mass boiler that can come from room temp to 160 or 180 in 1.5 to 2 min and cool back down not leaving energy in the boiler.
The idea is to make a boiler work like a hot air furnace which would not be heavy cast iron.
So theory schmeary, lets look at real world contests:
Against the old type cast boilers that sat hot all the time (still sold for some unknown reason) the cold start steel boiler used 40% less in identical tract homes. I went there in the late 1980s and visited the installer too.
Now that the cast boilers have adopted the modulating temps (ala Buderus etc) the steel cold start boiler only won by 40 gal in a similar recent test here. That was only two houses so it is not definitive yet. Close enough to call a tie. I would say that the type of system to choose would depend on the size and design of the house.
#24
Received 0 Votes
So, I am refining this install.
So far I am now going with the following
Burnham MPO 115 with Supply side Taco 007
Taco 3 zone control with priority
Super Stor Ultra 45 gallon indirect
Question is, will the MPO 115 be able to supply the 45 gallon indirect?
Specs are as follows
MPO 115 BTU 115,000
Super Stor Indirect (45 gallon) Says it needs a BTU of 141,000 ( for 180 degrees) or 161,000 ( for 200 degrees)
The only superstor tank that says it needs the BTU that is the same range as the MPO 115 output is the 30 gallon tank. Does that mean, that is the largest tank I can put with this boiler??
Maybe I am interpreting all this wrong?
I have a family of 4 with 2.5 baths in the house. We do have one soaking tub in one bath. Would a 30 gallon indirect be enough? I don't think there would be a problem since recovery time is short.
MPO 115 BTU 115,000
#25
Received 0 Votes
Yes it will. Those are the ideal specs. With priority, you will devote the full output of the boiler to making hot water for 10-15 minutes. Recovery should be fine.
FWIW, I fire a 96,000 boiler into one of the world's worst indirects, and it does fine.
#26
Received 0 Votes
I agree. I have done it without the hw priority and it works fine in a duplex with 2 apartments. I thought maybe we would come back and add the domestic hw priority control but they just cranked the temp up a little and had no problem.
#27
Received 0 Votes
This may be a really dumb question but I figure I had better ask anyway, in case there is something I am missing.
As I stated earlier in this thread, my boiler is about 14 feet from where the zone valves are located. This is due to the fuel line inlet in the garage.
Is there any issue with having the zone valve for the indirect water heater branch off the main supply line closer to the boiler? So the zone would be about 4 feet down the supply with the other zone valves being about 14 feet away.
To me it doesn't seem to matter but I thought I would check.
Thanks!
Thanks!
#28
Received 0 Votes
Thanks!
Thanks!
There can be some weird side effects of having a zone valve in a bad spot in relation to the circulator, but it will do its job anywhere in the branch line, it will offer the same restrictions to flow anywhere.
#29
Alaskanstar, I'll echo the need to carefully examine your zoning requirements. The whole concept of more zones in a house being more economical only exists when the home is poorly designed and/or constructed. Otherwise, the zones that aren't heating get heated by those that do and all you are doing is decreasing the load each heat call and increasing your cycling. Increased cycling decreases efficiencies.
The ideal for me is everything in one zone and in those spaces where you want to fine tune the heat, install TRVs. With an ECM pump and TRVs you'll have low pumping/circulation costs and incredible comfort.
I would use a separate and properly sized pump for your DHW.
#33
Received 0 Votes
Mpo 115
The MPO 115 is 98/85 MBH.
It is convenient now here for heat loss because the state of Alaska has a program for cash rebates up to $10,000 and loans up to $40,000 if you get an energy audit by a state certified rater who files a report on what you should do to improve your house. As you follow the guidelines recommended you get points toward the rebate. They do the whole blower door and thorough house exam.
As for pics, since I only replaced the boiler and not the existing zones and domestic hot water there is not much to show to separate my work from the old stuff.
It is typical of the houses in this climate.
Zones:
1- Living, dining
2 and 3 bedrooms
4- office
5- rec room
6- garage
Zones:
1- Living, dining
2 and 3 bedrooms
4- office
5- rec room
6- garage
#34
Received 0 Votes
This message is really focused for those on the board in Alaska.
I am wondering about state code on some boiler items and what is or is not required.
Low water cut-off?
Height of boiler off of floor?
Boiler bypass line?
System limit?
Thanks for any assistance.
Low water cut-off?
Boiler bypass line?
System limit?
#35
Received 0 Votes
State
The low water cut off is not required on residential here but it can't hurt.
In a garage or basement the burner needs to be 18 inches from the floor. You can get a stand at Fergeson which is a steel plate with 2" pipe for legs.
I most often just use concrete blocks, stacked 2 high with a 2" paver on top. That gives you 18" to the bottom of the boiler.
The bypass is not code but manufacturers instructions.
I just installed an MPO. The instructions say you must install a boiler bypass of the full size with a balancing valve.
I am now doing a Buderus which prefers a controlled mixing valve on the boiler bypass.
If you are in Fairbanks you can call me at 888-8322. I am working near S. Cushman
#36
Just for clarification the MPO only requires a boiler bypass since you have radiant zones. If this would be baseboard or zoned radiator system boiler bypass is not required.
The valve in the bypass is not a balancing valve it is a shut off valve. Since a boiler bypass sends cool return into hot supply you need to reduce the flow through the boiler and leave the bypass valve wide open. And yes keep the bypass pipe same size as the supply and return piping.