Dielectric Union Required?
#1
Member
Thread Starter
Join Date: May 2007
Location: Norfolk
Posts: 45
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Dielectric Union Required?
Stainless Steel manifold, copper supply and return lines.
Closed loop radiant system.
Do I need to put a dielectric union between the stainless and copper?
Thanks for any help.
Best regards,
Scott
Closed loop radiant system.
Do I need to put a dielectric union between the stainless and copper?
Thanks for any help.
Best regards,
Scott
#2
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Some people swear by dielectric unions. Some people swear that they cause more problems than they solve.
Stainless and copper shouldn't pose much of an issue. They are close to each other on the galvanic table.
I would opt for no dielectric union.
Stainless and copper shouldn't pose much of an issue. They are close to each other on the galvanic table.
I would opt for no dielectric union.
#4
Member
Join Date: Jun 2009
Location: Fairbanks Alaska
Posts: 83
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It is not needed on a closed heating system at all, even between steel and copper.
It is used on the domestic hot water between dissimilar metals because a fresh water system is constantly introducing new water. The hot side of a house domestic water system corrodes more than the cold.
It is used on the domestic hot water between dissimilar metals because a fresh water system is constantly introducing new water. The hot side of a house domestic water system corrodes more than the cold.