Dielectric Union Required?

Stainless Steel manifold, copper supply and return lines.

Closed loop radiant system.

Do I need to put a dielectric union between the stainless and copper?

Thanks for any help.

Best regards,
Scott
 
  #2  
Old 07-26-09, 11:09 AM
X
Member
Join Date: Nov 2005
Location: USA
Posts: 2,338
Upvotes: 0
Received 0 Upvotes on 0 Posts
Some people swear by dielectric unions. Some people swear that they cause more problems than they solve.

Stainless and copper shouldn't pose much of an issue. They are close to each other on the galvanic table.

I would opt for no dielectric union.
 
  #3  
Old 07-26-09, 07:43 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
Thumbs down

I'm in the second group. In my opinion dielectric unions are trouble just waiting to happen, especially in closed-loop systems.
 
  #4  
Old 07-26-09, 10:14 PM
B
Member
Join Date: Jun 2009
Location: Fairbanks Alaska
Posts: 83
Upvotes: 0
Received 0 Upvotes on 0 Posts
It is not needed on a closed heating system at all, even between steel and copper.

It is used on the domestic hot water between dissimilar metals because a fresh water system is constantly introducing new water. The hot side of a house domestic water system corrodes more than the cold.
 
  #5  
Old 07-28-09, 12:36 PM
S
Member
Thread Starter
Join Date: May 2007
Location: Norfolk
Posts: 45
Upvotes: 0
Received 0 Upvotes on 0 Posts
All,

"No" it is.

Thanks for the help. My gut told me I didn't need one, but my gut has gotten me into trouble before...